Here's the problem: I have a 400 ampere feeder (Fused at 400 amperew) and I'm taping to feed a 40 ampere load using a 60 ampere saftey switch and installing 40 ampere fuses to protect my 40 ampere load conductors. What size wire should I use from the feeder tap to the 60 ampere disconnect? (Using THHN in a damp location).


George Little
Work Gear for Electricians and the Trades

Workgear for Electricians

#88337 05/28/04 09:36 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Forgot to tell you the tap is 8 feet long.


George Little
#88338 05/28/04 09:46 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
I would say #8


Ryan Jackson,
Salt Lake City
#88339 05/28/04 10:02 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
George you ask some interesting questions. [Linked Image]

Assuming a lot here, but if all the requirements of 240.21(B)(1) are met I agree with Ryan 8 AWG copper.

Now one for you, or anyone, what size grounding conductor is needed from the point of the tap to the 60 amp disconnect?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#88340 05/29/04 12:20 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
but shall not be required to be larger than the circuit conductors supplying the equipment.


Don(resqcapt19)
#88341 05/29/04 05:55 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Yes, but the question remains. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#88342 05/29/04 08:38 AM
Joined: Nov 2000
Posts: 2,148
R
Member
The tap conductors are the conductors feeding the equipment and so the EGC is #8. Table 250.122 requires a #3 EGC for a 400 amp OCPD, but #3 is larger than the conductors feeding the equipment and the EGC is not required to be larger than the conductors feeding the equipment.
Don


Don(resqcapt19)
Work Gear for Electricians and the Trades

Workgear for Electricians

#88343 05/29/04 09:31 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
IMO a lot of people would size the conductor I am asking about based on the 40 amp fuse which would be 10 AWG copper which will be correct on the load side of that 60 amp disconnect.

I wanted to point out that the EGC on the supply side of the 60 amp disconnect will need to be based on the 400 OCP.

That would normally be a 3 AWG but for this application, will only need to be 8 AWG as the supply conductors are only 8 AWG.

I thought Georges example was perfect for pointing all this out, [Linked Image] only a little off topic.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#88344 05/29/04 09:37 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
FWIW I would wire this disconnect up with 6 AWG, the length is short the difference in price and difficulty will not be a big deal.

Besides all I do is order the stuff, I do not pay for it. [Linked Image]

JMO, not required, Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#88345 05/29/04 03:51 PM
Joined: May 2004
Posts: 19
D
dfe Offline
Member
I agree with Iwire
#6 for the full load amps of the 60/as ( in the future you could change the load without rewire the whole mess )
#10 ground
all wire thwn ( damp location )

As long as the total wire lenth of the tap is less then 10'