#87919 05/03/04 05:09 PM
Joined: May 2004
Posts: 3
R
rapahoe Offline OP
Junior Member
I have a new 300 kVA, 12.47kVwye - 480Vwye service transformer for a petroleum distribution facility that has existing cathodic protection system on underground pipelines. Local inspector has given verbal approval to use a cathodic isolation (PCR)module between neutral & grnd of service entrance to satisfy 250-6(e)and block the injected DC. Any special concerns for ground grid under pad mounted transformer or under the service entrance building (14' x 8') less than 10 ft. away?
Thanks!

2017 / 2014 NEC & Related Books and Study Guides
#87920 05/04/04 05:17 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Cathodic protection is its own beast so far a NEC-type systems are involved. Is it safe to assume that the 300kVA transformer is under the domain of the petrochem and not an electric utility? You might start by scrutinizing the listing instructions and, as needed, contact the “PCR-module” manufacturer for resolution. If this is new territory for the inspection authority, he may be easiest to work with if you approach him up front with as much PCR-specific application information as possible.




[This message has been edited by Bjarney (edited 05-04-2004).]

#87921 05/04/04 05:23 PM
Joined: May 2004
Posts: 3
R
rapahoe Offline OP
Junior Member
BJarney - Thanks! I have an inquiry in to the PCR manufacturer regarding grounding concerns and have provided a data package to the inspector. I was hoping to link up with someone else who had worked with the nuts and bolts of this sort of installation.

#87922 05/04/04 06:13 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
rapahoe — I didn’t mean to lead you astray and pretend I was any sort of CP whiz. I’ve found the “Leister golfcart battery chargers” in rural areas and see them indicating ~50 amperes DC disappearing into the ground over a set of mysterious cables.

One author of CP-application papers is John P Nelson in Colorado, with some online PDFs available at www.neiengineering.com/papers/papers.html

#87923 05/04/04 06:42 PM
Joined: May 2004
Posts: 3
R
rapahoe Offline OP
Junior Member
Bjarney, Thanks for the link to John's web site. I had the priviledge of meeting him in Denver a couple years ago.

#87924 05/04/04 07:08 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
[I’m not sure I would recognize a ‘Little FINK’ test station if I tripped over it.]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,438 Are you busy
213,522 Re: Forum
200,401 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5