ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Back From Retirement
by BigB - 08/15/22 08:36 PM
Upside Down ThreeWay
by gfretwell - 08/12/22 12:30 AM
Load Calcs for EVs and RVs
by gfretwell - 08/12/22 12:24 AM
Wiring method choice
by HotLine1 - 08/10/22 03:39 PM
NEC- 314.23 (H) (1)
by renosteinke - 08/10/22 11:13 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 32 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#87919 05/03/04 05:09 PM
Joined: May 2004
Posts: 3
R
rapahoe Offline OP
Junior Member
I have a new 300 kVA, 12.47kVwye - 480Vwye service transformer for a petroleum distribution facility that has existing cathodic protection system on underground pipelines. Local inspector has given verbal approval to use a cathodic isolation (PCR)module between neutral & grnd of service entrance to satisfy 250-6(e)and block the injected DC. Any special concerns for ground grid under pad mounted transformer or under the service entrance building (14' x 8') less than 10 ft. away?
Thanks!

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#87920 05/04/04 05:17 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Cathodic protection is its own beast so far a NEC-type systems are involved. Is it safe to assume that the 300kVA transformer is under the domain of the petrochem and not an electric utility? You might start by scrutinizing the listing instructions and, as needed, contact the “PCR-module” manufacturer for resolution. If this is new territory for the inspection authority, he may be easiest to work with if you approach him up front with as much PCR-specific application information as possible.




[This message has been edited by Bjarney (edited 05-04-2004).]

#87921 05/04/04 05:23 PM
Joined: May 2004
Posts: 3
R
rapahoe Offline OP
Junior Member
BJarney - Thanks! I have an inquiry in to the PCR manufacturer regarding grounding concerns and have provided a data package to the inspector. I was hoping to link up with someone else who had worked with the nuts and bolts of this sort of installation.

#87922 05/04/04 06:13 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
rapahoe — I didn’t mean to lead you astray and pretend I was any sort of CP whiz. I’ve found the “Leister golfcart battery chargers” in rural areas and see them indicating ~50 amperes DC disappearing into the ground over a set of mysterious cables.

One author of CP-application papers is John P Nelson in Colorado, with some online PDFs available at www.neiengineering.com/papers/papers.html

#87923 05/04/04 06:42 PM
Joined: May 2004
Posts: 3
R
rapahoe Offline OP
Junior Member
Bjarney, Thanks for the link to John's web site. I had the priviledge of meeting him in Denver a couple years ago.

#87924 05/04/04 07:08 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
[I’m not sure I would recognize a ‘Little FINK’ test station if I tripped over it.]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
295,022 Are you busy
226,690 Re: Forum
211,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5