pwr. prob #874
03/26/01 08:39 PM
03/26/01 08:39 PM
A
AFFELEC  Offline OP
Junior Member
Joined: Mar 2001
Posts: 5
DEKALB, IL, DEKALB
we are having a problem when they pug in a comm. vac. the computers need to boot like they have lost power the computers are on seperate cir from the recepts they are using for the vac. neutrals are not shared on the same cir in question either but they are multiwire cir . they also are share the same panelboard. the ups on the computer doesnt seem to sense the problem which makes us belive there is a noise issue . we are thinking iso xfrmr but would like other sugest. thanks kevin.

Work Gear for Electricians and the Trades
Re: pwr. prob #875
03/27/01 07:18 AM
03/27/01 07:18 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
is it possible that the vacuums draw is dragging the voltage down to levels the UPS will sense here?

[Linked Image]

Re: pwr. prob #876
03/27/01 10:14 AM
03/27/01 10:14 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,901
NY, USA
Kevin,

There's a couple of things I'm curious about.
Are you saying there's a problem with more than 1 computer? If so, are they on the same ups? At the same time? Always?
Does the UPS sound an alarm or beep?
How many times has this happened? You said they are not on the same multiwire circuit? on I'm just asking these things to get as clear a picture as I can.

Is is a long run from the panel? Never hurts to check tightness of connections.

Any power fluctuation that would affect the computer should be sensed by the UPS first. There could be something wrong with it (ups). If you're talking about 1 computer there could be some problem with it not related to the Vac. Or, you could have a voltage drop problem (for various reasons) and a ups problem.

Just tossing out some ideas.

Bill

Re: pwr. prob #877
03/27/01 03:24 PM
03/27/01 03:24 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I would also take a hard look at the equipment grounds from the computer receptacles and the vac receptacles all the way back to the service. A surprising number of computer problems crop up due to grounding problems. Computers reference the equipment ground but the UPS might not.

Please let us know what you find out.

Tom


Few things are harder to put up with than the annoyance of a good example.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 11
Popular Topics(Views)
249,267 Are you busy
187,202 Re: Forum
176,554 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9594 MB (Peak: 1.0919 MB) Zlib enabled. Server Time: 2018-09-19 00:17:15 UTC