Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 408 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#87102 01/22/04 01:46 AM
Joined: Apr 2002
Posts: 2,527
B
Moderator
US Electric utilities have an insane number of standards with respect to transformers, and if those of the distribution variety fail, the likelihood of a quick, cookie-cutter replacement is good.
http://standards.ieee.org/catalog/olis/dtransformers.html

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#87103 01/22/04 11:01 PM
Joined: Dec 2002
Posts: 308
E
Member
I think Andy is trying to ask:
"If my main panel is 200Amp main and i have a 100A subfeed, 30A stove, 40Amp range, 40Amp A/C, and (10) 20amp single pole breakers and still room in the panel to pull additional circuits can i do that? Or i will max out the panel?"

I think that is what he is trying to ask.

Edward


Thanks
Edward
#87104 01/23/04 06:33 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Yes that is what he is asking and I do not think it can be answered here with the info given.

We have no idea what the connected load of the 100 amp sub feed is, an AC unit with a 40 amp breaker does not draw 40 amps and 10 20 amp SP breakers do not draw 200 amps.

There are only two ways to answer this. [Linked Image]

1)Take real load measurements with an amp clamp. On a large job we would put in a data logger for a few days to a week.

2)Do the load calculations from the NEC.

I was just at a commercial job looking at a 400 amp panel with six 200 and two 100 amp 3 phase breakers in it (1400 amps total).

Was this panel maxed out?

I would have to say no as it has been that way for many years. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87105 01/23/04 08:56 AM
Joined: Jan 2004
Posts: 79
C
cavo148 Offline OP
Member
Actually, what Andy is asking is how would you determine if this panel or any existing residential panel is maxed-out already, per the NEC. I believe to be absolutely sure I'd have to take the current readings for actual demand and calculate (per NEC) the pool equip. and the A/C equip. loads, since it's off-season for them. This overall existing load together with calculated load of the future living space should tell the story.

For business sake, we'd want to sell an upgraded service if justified, right? But, maybe our competitor is hinting that it's not really necessary for the additional circuits. Now you have to make your case.

What's your opinion?
Andy