#86842 12/19/03 05:27 AM
Joined: Sep 2003
Posts: 60
G
gunther Offline OP
Member
A guy I work with was installing an in cabinet dishwasher. He had already supplied an MC cable to feed it. The dishwasher came with an installed appliance cord with cord cap, all ready to go when plugged in. He was asking if he should go to the trouble of removing the cord and hard wiring it or do it the easy way and install a recepticle. He also wanted to know if he installed a recepticle, would he need to change the breaker to 15 amps. I told him I would look for it in the code. Any suggestions?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#86843 12/19/03 07:26 AM
Joined: Oct 2000
Posts: 5,392
S
Member
gunther;

i think you may find that the make cord cap provides a means of disconnect for the motorized unit , which usually will not accept loto...of course if the service panel is in the kitchen the point it moot...

#86844 12/19/03 04:28 PM
Joined: Jan 2002
Posts: 1,457
E
Member
Install a receptacle. No need to change to a 15 amp circuit unless required by manufacturer.

#86845 12/22/03 09:36 PM
Joined: Jun 2003
Posts: 681
P
Member
The listing for the dishwasher is most likely for cord installation. While reading the wiring installation instructions, you will be able to determine if you can remove the cord and hard wire it.
422.34 is usually appropiate for disconnecting means of a dishwasher.

Pierre


Pierre Belarge

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,471 Are you busy
231,870 Re: Forum
216,491 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5