#86679 11/19/03 09:25 PM
Joined: Aug 2001
Posts: 464
Likes: 1
J
Jim M Offline OP
Member
I was just in a older (about 30-40 years) house that I think has metal framing. It appears that the wiring was 2 conductor NM. A ground wire has been run between the box and the device. It seems like they were using the framing to achieve the ground connection. A plug-in checker shows the devices are wired properly. I don't think that this is the way it should be, but don't have enough info to make an informed decision. What options should I tell the owner are available?

Thanks,
Jim

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Oct 2000
Posts: 5,392
S
Member
first off~ this may have been compliant to the '63 nec....

secondly, there are newly marketed goodies to enhance the safety of older wiring, such as AFCI's

btw~ i would be very careful to offer anything more than 'enhancement' with these...

Joined: Mar 2001
Posts: 2,056
R
Member
I'm not a construction expert, but metal framing on a 30-40 year old house seems unusual.
Maybe the boxes are grounded but you can't see it. From behind?

Joined: Aug 2003
Posts: 1,374
R
Moderator
I would be very concerned if the framing of the house is used as an equipment grounding conductor...


Ryan Jackson,
Salt Lake City
Joined: Mar 2001
Posts: 333
S
Member
Jim, some of the old houses I deal with, use a small(16 gauge?) bare copper wire that runs throughout the house, "connected" to the boxes by wrapping several turns around a nail that attaches the box to the stud. The wire would terminate at a water pipe with a strap. The wire is tee tapped, by wrapping the tap around the main wire and soldering, just like knob and tube wiring. Sometimes it's just the kitchen and bath that have the wire.


Steve
Joined: Jun 2003
Posts: 681
P
Member
Using the structural steel, or a grounding conductor that is not run with the phase conductors may not ensure that the ground fault current path is effective.

250.4(A)(5) Effective Ground-Fault Current Path. requires this path to be effective, therefore that would not be a proper method.

I know that the code permits a grounding conductor to be run to the nearest equipment grounding conductor, 250.130(C), but I say this is asking for trouble.

Pierre


Pierre Belarge
Joined: Oct 2000
Posts: 4,067
Likes: 3
Member
Quote
some of the old houses I deal with, use a small(16 gauge?) bare copper wire that runs throughout the house, "connected" to the boxes by wrapping several turns around a nail that attaches the box to the stud
Stamcon,

I've seen that too, usually for Kitchens. Never seen Copper though, the ones I've seen seem to be Aluminum. They sometimes go from each device box up to the attic and are twisted together, or joined by some other questionable means. Many times these wires are cut or broken and not repaired simply because no one knows what they are.

I had some pictures around, but can't seem to locate them right now.

Bill


Bill
Joined: Dec 2000
Posts: 4,289
Member
Is there no ground wire at all?
All the metal boxes in my house were grounded with a bare #12 that was daisy chained from the back of one box to the back of another, then to ground in the service.
It wasn't run with anything else,just by itself. It apparently was Code compliant at the time ('58). I've seen lots done this way.

Joined: Oct 2000
Posts: 4,067
Likes: 3
Member
Here's a Photo sent to me by Joe Tedesco showing a Ground wrapped around a nail:

[Linked Image]


Bill
Joined: Jun 2003
Posts: 681
P
Member
Look at the nail going through the lower portion of the gem box.

Pierre


Pierre Belarge
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 240
Joined: March 2005
Top Posters(30 Days)
dsk 3
Popular Topics(Views)
297,767 Are you busy
228,511 Re: Forum
213,342 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5