I was asked by a local electrical contractor to stop by their shop and help train the electricians on service/grounding/bonding sizing.

Please take a minute and review this drawing I created. PLEASE let me know if you find any errors in it. Thank you.

[Linked Image]

[This message has been edited by Ryan_J (edited 11-10-2003).]


Ryan Jackson,
Salt Lake City
Horizontal Ad
#86558 11/10/03 06:31 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Ryan,
You don't have enough 600 kcmil cables for a 1600 service. You need 4 sets, which changes the line side bonding jumper to 300 kcmil.
Don


Don(resqcapt19)
#86559 11/10/03 06:33 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline OP
Moderator
EEK!!!!!

Thats why I posted this! I used the same diagram here that I used for a 1200A!!!

I had this for a 1600A, then I deleted (1) pipe on the feeder and one on the service entrance conductors, but I overlooked changing the rating of the fuses! (embarrassed)

thanks Don!