#86479 11/06/03 09:07 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Other than exothermic welding, what other methods are permitted to connect the #8 to the rebar in an inground pool?
I am aware if the Greaves "Jones Bond" system, but is there another acceptable technique?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2001
Posts: 717
G
Member
Redsy,
For a lot of years, we were allowed to tie wire the conductor to the rebar. That's a BAD method as the steel tie wire has a tendency to go away.

Mechanically, a split bolt is still acceptable, if you're using #4 rebar, you need a 1/2" split bolt (Like light bulb designations, rebar is sized by how many 1/8" increments - ie: #4 = 4 X 1/8 or 1/2")

ALL mechanicals are subject to failure, they are getting weaker the day you put them in. Add Chlorine, lime and all other chemicals associated with pools and concrete the subject grows quickly.

I gave up anything but cadwelds long ago, I've had to dig up too many pools where the other methods were used - NOT installed by me though. If you go with the mechanical methods, take a lot of care in the prep.
www.erico.com
they can get nearly any mold to you PDQ

Joined: Aug 2003
Posts: 1,374
R
Moderator
Wouldn't a listed Ufer clamp work?


Ryan Jackson,
Salt Lake City
Joined: Nov 2000
Posts: 2,148
R
Member
I don't believe that a split bolt is listed for that application.
Don


Don(resqcapt19)
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
How about an acorn that is listed/labeled for direct burial?

BTW,
The Greaves "JonesBond" connectors seem to be the best listed mechanical method.
I'm having trouble finding a local supplier that stocks their stuff.
I may have to order a whole box.

Joined: Aug 2003
Posts: 1,374
R
Moderator
When I write on an inspection report that something needs to be listed I am very careful to write "listed for the purpose". I think an acorn clamp could be used if listed for rebar attatchment. I think a listed Ufer clamp is the best bet, and that is what I require in the feild.


Ryan Jackson,
Salt Lake City
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Ryan,
The Ufer installations I've seen were either a compression "C"-tap or a water ground with one half reversed like this -- {{.
Do you have a picture of a listed Ufer ground clamp?

Joined: Aug 2003
Posts: 1,374
R
Moderator
Redsy: I don't have picture but I will take one tommorrow. I see them everyday here.


Ryan Jackson,
Salt Lake City
Joined: Aug 2003
Posts: 1,374
R
Moderator
Redsy: I want to make sure you realize I'm not blowing you off here. I looked the other day for a clamp, but I didn't ahve much time to hunt for one. I have a four day weekend and will spend half of the day Wednesday at IAEI board meetings. Hopefully I can get a picture for you Wednesday or Thursday. Sorry [Linked Image]


Ryan Jackson,
Salt Lake City
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Thanks, Ryan.

I will wait patiently. [Linked Image]