rating of disconnect #86294 09/30/03 06:55 PM
Joined: Aug 2003
Posts: 99
richard Offline OP
Member
My boss sent me to relocate 2 a/c feeds, rooftop units. The existing units have 90 amp breakers on #4 thhn. The new units have the need for 60 amp, so since the brekers for the original units are hard to get, and expensive, a 3 phase disconnect (100 amp) with 60 amp fuses, (mounted on the unit) will protect the unit. One of the mechanics at the shop thought you could get away with a 60 amp fused disconnect, but I say that you have to go by the rating of the highest amperage. I only have the handbook at home, but I don't see a reference to this. Also, if one of the fuses lets go, will the unit burn up? (becasue of running on single phase?) Thanks for any help on this.

2017 / 2014 NEC & Related Books and Study Guides
Re: rating of disconnect #86295 09/30/03 07:02 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
You can go either way with this it is your choice.

In industrial applications it is not unusual to run a large feeder 400, 600, etc and have a group of disconnects tapped off of these of any size.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: rating of disconnect #86296 09/30/03 07:20 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
One thing I forgot to mention is if you do go with the 100 amp disconnect you will need fuse reducers to get 60 amp or smaller fuses to fit in a 100 amp switch.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: rating of disconnect #86297 09/30/03 07:21 PM
Joined: Aug 2003
Posts: 99
richard Offline OP
Member
I guess what I meant to ask, Should there be a 100 amp rated disconnect,with 60 amp fuses, or can you get away with using a 60 amp disconnect with 60 amp fuses. The # 4 thhn is protected by a 90 amp breaker in the main switch gear.

Re: rating of disconnect #86298 09/30/03 07:23 PM
Joined: Aug 2003
Posts: 99
richard Offline OP
Member
yes i got the reducers

Re: rating of disconnect #86299 09/30/03 07:33 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
The 60 amp disconnect is fine. The 90 amp breaker protects the wire to the line side of the disconnect. The 60 amps fuses protect the load side wire and the equipment.
Don


Don(resqcapt19)
Re: rating of disconnect #86300 09/30/03 07:34 PM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Richard,

I haven't poked my head inside an AC unit in years, so I don't know if it comes built-in now but you can get phase loss protectors and add them yourself if necessary. I think it's a good idea.

Bill


Bill
Re: rating of disconnect #86301 09/30/03 07:41 PM
Joined: Aug 2003
Posts: 99
richard Offline OP
Member
Thank you all for getting back so quickly. Have you noticed that on the rooftop units, the available space for the disconnects are very limited?

Re: rating of disconnect #86302 09/30/03 07:46 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Nope their is plenty of space as long as you do not mind screwing the disconnect to the condenser coil. [Linked Image]

Yes it is hard to find space.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,021 Are you busy
205,021 Re: Forum
193,132 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3