Service grounding #86116 09/11/03 06:53 PM
Joined: Sep 2003
Posts: 114
B
bwise121 Offline OP
Member
I'm helping a friend upgrade two panels on a duplex he owns. The panels are right next to eachother. Each panel will be 100 amp.
The plan is to go up with one riser rated for 200 amp and bring that into a gutter. From the gutter, split into two 100 amp panels below.

I'm familiar with grounding for regular single family homes, but in this case I'm not sure if I'm needing to double up all the grounding.

I don't have a ufer so I'll use the water main as the main grounding electrode (it is metal going into the ground), secondary electrode will be a 8' ground rod. Lastly, I'll bond the gas at the hot water heater. All of this will be done in #4 bare wire.

This being said, I'm sure I don't have to put in two ground rods and run two #4 wires to the water for each panel. How is this normally done?

Any suggestions or advice on this would be appreciated... also, what is the differnece between grounding and bonding?

Thanks,

2017 / 2014 NEC & Related Books and Study Guides
Re: Service grounding #86117 09/12/03 06:13 AM
Joined: Feb 2003
Posts: 197
Z
zapped208 Offline
Member
What is a ufer? We do not use that term here in Pa or Ny. Thanks.


Shoot first, apologize later.....maybe
Re: Service grounding #86118 09/12/03 08:30 AM
Joined: Aug 2003
Posts: 2
J
jnsells Offline
Junior Member
The grounding electrode conductors can be spliced together in the gutter, then one grounding electrode conductor run to your grounding electrode(s), with the size based on a 100 amp service. Of course, the gutter has to be bonded also. Soares book on grounding has good illustrations of this.

Although the code requires gas piping to be bonded, several AHJ's and local gas companies will not allow this.....best to check first.

For our friends in PA & NY, a UFER is a concrete encased grounding electrode, typically rebar within the foundation. The UFER ground system was actually developed during World War II by Herbert G. Ufer, a retired vice president of U.L.

Re: Service grounding #86119 09/12/03 07:05 PM
Joined: Sep 2003
Posts: 114
B
bwise121 Offline OP
Member
Although some interesting comments I'm not finding this helpful.
Example of the kind of explaination I'm looking for follows:
Take the Grounding electrode and the conductor from the ground rod to one panel then take a grounding jumper from the first panel to the second panel.

Please reply,
Byron

Re: Service grounding #86120 09/12/03 09:12 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
If it's do it yourself info you need you might be in the wrong place. By the way where are the meters? I can think of no reason to have a gutter.

Re: Service grounding #86121 09/12/03 10:53 PM
Joined: Oct 2000
Posts: 2,721
Scott35 Offline
Broom Pusher and
Member
I agree with Electricmanscott, especially since jnsells' post answers the question concisely.

Sorry if this sounds offensive (which it's not intended to be at all!).

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Service grounding #86122 09/12/03 11:55 PM
Joined: Sep 2003
Posts: 114
B
bwise121 Offline OP
Member
No offense taken. I guess I was looking for someone to say point A goes to point B. I have purchased some electrical books and I am educating myself. This is a very useful board and I intend to use it in the future.

As for the gutter, I'm only following the advice of fellow electricains that have done similar work. I guess the idea is to have one riser. The existing panels are right next to eachother, so it would make sense for the riser to come into the gutter and then each conductor into a landing lug then to the line side of meter.

Sound okay?

Many thanks and have a good weekend.

Byron

Re: Service grounding #86123 09/13/03 01:44 PM
Joined: Jun 2003
Posts: 681
P
PCBelarge Offline
Member
Byron
Your bio does not state your occupation, I am curious why? This leads the pros here to be cautious as to how much info they give, because all the info given to a novice or homeowner will still not be enough. There is so much more to this industry than point A to point B!

Pierre


Pierre Belarge
Re: Service grounding #86124 09/13/03 02:34 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
For a two family I would use a 2 gang meter socket. One 200 amp riser from that, a hundred amp feeder to each panel. I see no need for a gutter at all. This is all the info I can give as this is NOT a do it yourself project and while it is good to see you trying to learn, this board and some books are not going to make you an electrician. If I lived in that duplex I would not be happy to know the wiring is being done by some handymen. In fact I would notify the local authorities.

Re: Service grounding #86125 09/13/03 02:57 PM
Joined: Sep 2003
Posts: 114
B
bwise121 Offline OP
Member
LOL very funny. Sorry to misguide you as to thinking I'm a handyman by the fact that I'm helping a friend out. I'm a licensed electrician here in California. This isn't my expertise so I was trying to find some info on grounding multi-family homes. I mostly have done commercial and single family homes. Again, the idea of a gutter with two 100 Amp panels was new to me and thats what I was told to do by fellow electricians as stated in a previous post.


Byron

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,060 Are you busy
205,042 Re: Forum
193,167 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3