Joe: Not to keep beating a dead horse, but:
"The stands are put up early on Friday afternoon and taken down last on Saturday afternoon, 52 week a year!!"
Are you saying the structure is physically taken down, or that the products and tables are removed???
From your pics, the stand looks like a very substantial structure to be dis-assembled.
IMHO, I would request that a safer arrangement for power and lighting be installed. A "transient" market that is in the same location does not qualify for "temporary" wiring status. The vendors may be "temporary" but a "market" that is there 52 weeks a year is permanent.
I have to check with a few AHJ's in the towns that have permanent, year-round flea markets, and get some opinions.
John
John
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
Joe,
Is there someone there who sells beef? Maybe he can throw a steak at you? Then as John said, you might make yourself a great meal! Seriously though, this temp. wiring can get out of hand. I saw a pine tree with holiday lights on it that was left uo for at least 5 years. The town owns the property and the tree and the lights. I told the town that the temp string of Christmas lights were looking a little bit frail and should be taken down. These were holiday lights and as such, they were suppose to be removed under sec. 350 (Back when I was there) of the NEC. The town still has the same string of lights on the tree, and I haven't worked for this town, since before 1998.
|
|
|
|
Joined: Apr 2002
Posts: 197
Member
|
Why does almost everyone believe "any goes" for Temporary Installations"?
Please read 527.2(A) s-l-o-w-l-y.
Gwz
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Joe: OK, I guess they "take down". Based on that, a safe and Code compliant wiring method would have to be employed/designed.
Also, the lighting would need "lamp" protection to pass muster (not muenster) here in NJ. At a minimum, silicone coated, shatter resistant a-lamps, & the duct tape would have to go.
Using duct (or gaffer) tape to secure cabling for a two day use would be acceptable, providing that there was no possibility of physical damage to the cables. Taping the fixtures together, "temp" or not would not fly!
As to the "extension cords" laying on the ground, protection from physical damage, and the use of the cords has to be addressed. GFI and twistlocks?? A "permanent" power source for the "stands" can be installed, with receptacle outlets at the "stand" locations, or EHD cords with caps layed out & PROTECTED by cable covers also would be acceptable.
Alas, the solutions are "dreams"; the answer would be "we've been doin' it like this for years!"
John
John
|
|
|
|
Joined: Aug 2002
Posts: 1,691
Member
|
I don't quite understand why they covered the octagonal handiboxes and the fixtures with the duct tape like that.
Was it a lame attempt at water-proofing?
Anyone know how conductive that silver duct tape is? I assume it's got traces of aluminium or something in it....
I know this is not NEC related, but how smart is it to use a 200 watt lightbulb in base-up position? Those things do look like 200 watters (the ones I see usually have long necks although I once saw large 100 watt and 75 watt bulbs like that too).
[This message has been edited by SvenNYC (edited 09-14-2003).]
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
please start enforcing it.....
|
|
|
|
Joined: Apr 2001
Posts: 518
Member
|
Had another thought: Treat the entire stand as though it were an appliance, and apply criteria similar to UL standards.
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
The vendor threw a potato at me... Good thing he wasn't selling eggs... HotLine1: pass muster (not muenster) Mustard?
|
|
|