ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photos of the Week:

Avalon Theatre
Avalon Theatre-1 2 3 4

Random Gallery Image:
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 135 guests, and 33 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#85979 08/24/03 04:19 PM
Joined: May 2003
Posts: 2
S
Surge Offline OP
Junior Member
In reference to Table B310-11, what exactly does a 50% load diversity mean?

Horizontal Ad
#85980 08/24/03 10:49 PM
Joined: Feb 2003
Posts: 138
W
Member
The factors in the second column of Table 310.15(B)(2)(a) are based on no diversity, meaning that all conductors in the raceway or cable are loaded to their maximum rated load. For load diversity, the user is directed to Annex B.


Dave
#85981 08/26/03 10:01 PM
Joined: Mar 2001
Posts: 2,056
R
Member
IMHO,

I always took it to mean that the average loading of all the wires in the conduit was at about half the total calculated load.
However, now I'm wondering if my reasoning is circular. Maybe it's one of those things that you think you understand, but can't explain it.

For example,

If 12 #6 THWN copper conductors (basic ampacity, 65 amps per Table 310.16) are installed in a single conduit, Table 310.15(B)(2)(a) requires a reduction to 50%, or 32.5 amps.
If it can be shown that, at any given time, either half of the conductors would be carrying no current while the others are fully loaded, (or another combination of percentages that would equal the same total current) you are permitted to alter your adjustment factor up from 50% to 70%, for an increase from 32.5 to 45.5 amps.


Link Copied to Clipboard
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5