Joined: Aug 2002
Posts: 47
F
Member
I need a little help reguarding the 6 ft rule on gfi protection. I am purchasing a house built in 1990 and none of the outlets in the house are gfi protected. I noticed this on a walk through inspection and it was written up on a home inspection report as well. The current owners refuse to install the necessary gfi protection stating that it was the local building departments fault because the home passed inspection at the time it was built.

I am trying to verify when this rule was adopted into the code. The earliest code book I have is the 1996. Does anyone have a copy of the 1987 book?

Thanks

fla sparkey

Horizontal Ad
Joined: Oct 2000
Posts: 4,160
Likes: 5
Member
210-8(a) in the 1987 NEC required GFCI protection for kitchen countertop receptacles within 6 ft of the sink as well as Basements, Garages, Bathrooms and Outside.

And in the 1984 NEC it was required in Bathrooms, Garages and Outside.

Bill


[This message has been edited by Bill Addiss (edited 06-30-2003).]


Bill
Joined: Aug 2002
Posts: 47
F
Member
Thanks Bill.

I verified it as far back as 1978 on the bathrooms, garages, and outside recepts. I just needed to find out what year it was required within 6 ft of the sink. I thought it was 1987 but couldn't prove it. This clears things up a bit.

Sorry I posted the question in the general discussion area first.

fla sparkey

[This message has been edited by fla sparkey (edited 06-30-2003).]

Joined: Oct 2000
Posts: 4,160
Likes: 5
Member
1 demerit so far ....
just kidding. [Linked Image]

So, I guess you have confirmed that the 1987 NEC is what was used at the time? Just curious as I know some areas are slow to adopt sometimes. But that would only affect Kitchens and Basements, no excuse for the rest of the house.

Bill


Bill

Link Copied to Clipboard
Advertisement:-Right
Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
561,583 Are you busy
435,235 Re: Forum
404,033 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5