1 members (dsk),
1,418
guests, and
21
robots. |
|
Key:
Admin,
Global Mod,
Mod
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Here in So CA, land of "sticks & stucco", these aren't considered to be fireblocks at all. The requirements for blocks are 3 from a corner, and 2 from an opening (door, window, etc). We're required to seal holes in exterior walls (for insulation reasons), but not interior, unless they're through the wall's top or bottom plate. Since RX isn't rated for any firewall penetrations, I can't remember the issue of firecaulking around it ever coming up.
|
|
|
|
|
Joined: Jun 2001
Posts: 642
Member
|
A lot of times when we do a single family house, fire caulking is not enforced by the structural inspectors. When we do apartments it is always enforced. The electrical inspectors here do not look at fire caulking leaving it to the structural inspectors. This is because more than electricians make holes in framing.
ed
|
|
|
|
|
Joined: Aug 2002
Posts: 1,081
OP
Member
|
Well, so far, my neighbor was told "no fireblocking is needed at all" when he called to ask. The GC went in person and was told that it is needed, first floor only. nesparky: ...more than electricians make holes in framing. Yep. I believe (I may be wrong...) water pipes, especially heating/hot water pipes, need space around them to allow for expansion/contraction of the copper and to prevent noise from banging.
|
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
You might do a google search for “intumescent caulk”.
|
|
|
|
|
Joined: Aug 2002
Posts: 1,081
OP
Member
|
Man, there you go with that intumescent vocabulary!
|
|
|
|
|
Joined: Mar 2003
Posts: 22
Member
|
Fire caulk (from what I've learned) is only required in holes that have been drilled from one unit to the next unit. Example: If you have an apartment, where you have someone living above you,and holes are drilled between floors,then you would have to fire caulk those holes made between units. Note: if the the floors in the unit are in the same dewelling (meaning: the aparment has and upstairs, and down stairs), then you would only use foam.
|
|
|
|
|
Joined: Jun 2001
Posts: 161
Member
|
Here in Nevada we have these in all new homes. When we bore a hole in them we are also required to seal them. We can use intumescent caulk, or fiberglass from fiberglass insulation jammed in the holes, or regular cualk on both sides.
Mike Wescoatt
|
|
|
|
|
Joined: Oct 2001
Posts: 9
Junior Member
|
The International Building Code requires the holes in firestops to be sealed. It's usually done by the insulation compane.
|
|
|
|
|
Joined: Oct 2000
Posts: 4,165 Likes: 7
Member
|
I just came across the following while browsing the Michigan Rehab Code for Existing Buildings 109.3.4 Frame inspection. Framing inspections shall be made after the roof deck or sheathing, all framing, fire blocking and bracing are in place and pipes, chimneys and vents to be concealed are complete and the rough electrical, plumbing, heating wires, pipes and ducts are approved. Is this the procedure followed where you are? I think that the Framing Inspection where I am is often done before any other Trades get in there. What is the norm? Bill
Bill
|
|
|
|
|
Joined: Jun 2001
Posts: 642
Member
|
Around here the framing inspector will not show up untill the electrical HVAC and plumbing inspectors have signed off thier rough ins. If called they look on the plans to see the rough in stickers (the Gc is required to have approved plans on job site), if they are not there the framing inspector red tags job as not ready for inspection and walks away and charges the GC with a re inspection fee.
ed
|
|
|
Posts: 61
Joined: August 2007
|
|
|
|