Does the NEC specifically state that service conductor shall be USE or SE cable? If so, please state article number. Thanks

Work Gear for Electricians and the Trades

Workgear for Electricians

#84597 04/14/03 11:52 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Individual Service Conductors in raceways may be of a type that is suitable for environment encountered (usually wet locations). As far as cables such as NM or UF, their specific articles (334.12, 340.12, respectively) state that they are not permitted to be used a service-entrance cable.

#84598 04/14/03 08:24 PM
Joined: Oct 2000
Posts: 2,749
Member
See also 230.43


Joe Tedesco, NEC Consultant
#84599 04/18/03 02:31 PM
Joined: Feb 2003
Posts: 67
P
Member
see also 310-15(b)(6)