1 members (Scott35),
166
guests, and
12
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jan 2003
Posts: 59
OP
Member
|
Up comes another- where does it say that a ground rod right beside a cold water bond on the water supply cancels the 2 seperate ground issues? I thought I had it right before.......
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
CCDave: Could you be a little more specific please. The "issue" with 2 ground rods is 250-56 ('99 NEC); unless testing & documentation that 1 rod is 25 ohms or less.
What's the rod have to do with the water pipe, before the meter?? John
John
|
|
|
|
Joined: Jan 2003
Posts: 59
OP
Member
|
I have contractor that is insisting that the rod beside the water pipe is wrong.That it should be by the panel in back and the water bond goes to the front where the supply comes in within 5ft.
|
|
|
|
Joined: Oct 2002
Posts: 210
Member
|
The water bond and using the water pipe as a grounding electrode are two different issues. If your able to use the water pipe as a grounding electrode, then yes the connection is required to be within 5ft of where it enters the building and it must be supplemented with at least one additional ground rod. The 5 ft rule is good practice even if the cold water is not used as a gronding electrode. This way if a water pipe is cut or removed you do not lose your water bond and possibly grounding electrode.
|
|
|
|
Joined: Jun 2001
Posts: 642
Member
|
As spyder said the ground rod and the water pipe are seperate issues. There is no requirement on where you locate the ground rod as long as it is installed correctly wired correctly and in a suitable location. It could be by the panel and usually is around here. Where the water pipe comes in is a different subject.
ed
|
|
|
|
Joined: Jan 2003
Posts: 59
OP
Member
|
Actually after talking to him again he is saying that you cannot put the grd rod beside the water pipe, it must be by the panel sereratly?
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
The code does not specify the location of the ground rod. There is no reason either from an electrical standpoint or a code standpoint that a rod cannot be installed next to the metal water pipe. Don
Don(resqcapt19)
|
|
|
Posts: 3,682
Joined: October 2000
|
|
|
|
|