ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#84105 03/10/03 02:54 PM
Joined: Apr 2002
Posts: 178
R
Member
Can someone please give some advise on this.Running wiring through holes in a web beam floor joist.I don`t have them packed but I have 4- 14/2 cables in some and 12/2 and 10/3 in others and ahj says I`m bundling must derate.I thought they had to be tied or taped. Thanks

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84106 03/10/03 05:00 PM
Joined: Oct 2000
Posts: 5,392
S
Member
'bundeling' is somewhat ill-defined, 310.15(b)(2)ex 5 can be used if your running MC or AC.

Table 310.15(b)(2)(a) w/310.16's ability to start @ the 90 deg collum should grant you some leverage

#84107 03/10/03 06:03 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
If all you have is four 2 wire cables, there is no problem. You will be derating to 70% of the 90 degree column.

The trouble starts when you hit the fifth 2 wire cable in the bundle which requires a 50% derating.

As for the 3 wire cables, if this is a single phase system, the neutral is not considered a current carrying conductor and if this is a 3 way switch cable, only 2 wires are current carrying.


Few things are harder to put up with than the annoyance of a good example.
#84108 03/10/03 07:46 PM
Joined: Feb 2002
Posts: 375
G
Member
Only if the joist holes are longer than 2' does the derating apply.

It is between you and your inspector as to what you will agree on.