Commercial office building, 7 stories above grade, in NY State. Follows the 1999 NEC. What are the restrictions to this installation. Does it follow the NM article restricting this to buildings at or below 3 stories and the support paragraph? If not, how many feet bewtween support of the cable is required?
Note: This has also been posted to Holts site, without much activity.
Ron
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
Ron,
Have you tried searching New Yorks code online?
http://www.nyc.gov/html/dob/html/code.html
OOOPS--That link is for NY city.
[This message has been edited by txsparky (edited 03-07-2003).]
Donnie
Ron Offline OP
The New York State code follows the IBC and NFPA 70 1999.
Ron
Ron,
Here in Ohio, we pretty much go by the National Fire Code. We also need to be licensed, submit plans and pull permit to add or modify systems.
Is NY the same?
Dave
[This message has been edited by WebSparky (edited 03-07-2003).]
Dave
Ron Offline OP
Permit and plans are the same. NY State follows NFPA 72 for Fire Alarm Code.