Wiring a metal storage building 200amp service six 8' lights and 1 rec IS this rec required to be gfci protected?Can`t remember readind this in code ajh says yes but didn`t furnish art number. Thanks
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
If this is at a residential occupancy, then 210.8(A)(2) requires the receptacle to have GFCI protection. If this is not a residential occupancy, GFCI protection is not required by the code. Don
Don(resqcapt19)
|
|
|
|
Joined: Apr 2002
Posts: 178
OP
Member
|
Don thanks for the reply here`s what the ajh said this am. It is a commercial storage building behind a gun shop but he said with it having 2 roll up garage doors he quoted 511.12. I hate to fight out with him but the guy already has shelfs and it`s pretty clear it`s a storage facility and not a garage.Just thought I`d completely missed something in the code thanks again.
|
|
|
|
Joined: Feb 2003
Posts: 138
Member
|
Hi Reel-Break,
Personally, I always think of personel safety when I wire garages and commercial buildings. So as a result, I am always wondering why installing a GFCI is a big deal. Given that the NEC is a minimum requirement for electrical safety, why do some contractors in certain situations opt for no GFCI? I do not mean to sound disrespectful, I honestly don't understand.
Thanks, Dave
[This message has been edited by WebSparky (edited 02-26-2003).]
Dave
|
|
|
|
Joined: Apr 2002
Posts: 178
OP
Member
|
Hey Web sparky, It`s not a big deal.It`s a matter of $ That could have been my lunch today.Also I done a job that was code compliant and the inspector turned it down for the wrong reason leaving the storage building guy with a question of my work.But I always try to do my work neat and in most cases more than code worthy.I talked to AJH and I actually did put a gfci in but it cost me time and $8.00 No offence taken. Should gfci`s be put everywhere....no whats the difference.Are they safer everywhere...most likely.Thanks
|
|
|
|
Joined: Feb 2003
Posts: 138
Member
|
Reel-Break,
I have been in that situation myself on a few jobs years ago. After being embarassed in front of the customer, I just started explaining the benefits of a GFCI when I was selling the job and myself as an electrical contractor. When I was successful and sold the job based on having the customer's best interests at heart, the job always ended up with a happy customer and me making my profit margin. I know at times it sounds idealistic, but if we don't educate the customers, who will?
Thanks for not taking offence! Dave