Is there a NEC code that requires conduit runs with fiber to have junction boxes at every 100ft intervals.

Thanks for your help

Work Gear for Electricians and the Trades

Workgear for Electricians

#83468 02/03/03 05:07 PM
Joined: Nov 2000
Posts: 2,148
R
Member
No, there are no code rules about the distance between junction boxes or pull points. The only code rule is that you cannot exceed 360° of bend between pull points. The fiber run has to be designed to limit the pulling stress on the fiber, however, excessive pull points increase the chance that the fiber will be damaged when it is installed.
don


Don(resqcapt19)
#83469 02/04/03 08:16 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
I think there are installation standards from TIA/EIA and BICSI regarding pull points.


Ron