joe20, CTwireman,
I haven't the permission to fix anything, yet. I was there to install a transfer switch and cord to a generator. The pix were taken before I started, so now the lines and loads of the transfer switch unit are crowding the panel.
sparky, yup, you know it! Rock and a hard place, indeed! But there's more to this story... (in a minute)
Redsy, LOL! Well, he obviously had the knowledge to flag himself, he was the first IAEI certified inspector for electrical services required by the PoCo in this area.
Tom, you nailed it! This 200A 4 wire feeder comes from a disconnect that is paired with another panel and disconnect to a 320A meterbase. The EGC and Neutral need to be seperated here, and everything on the service end of thigs in pic #1 is OK
except he (they) neglected to remove the bonding bar between the busses. Then, in turn, someone made up all the EGCs and neutrals in the branch circuits with disregard to which bus they were on.
The bus bonding-bar needs removed and the EGCs need to go on the left and noodles on the right.
Everyone,
To better my arguments to have this (pic #1) corrected, what safety issues are compromised here?
Pearlfish, Chris is correct, this is a standard GE 200A 2 Pole Main CB. The individual breakers are really 100A, but two parallel per side for 200A per leg. Look closer at the bus feed below the Main CB.
John (Hotline1), Certified IAEI... The same one that likes to retorque my terminals.
(Things are looking up, I'll elaborate in another post...)
ElectricmanScott, Actually, this may have some interesting financial incentives...
NJWirenut, yes there is a white stripe (not visible in pic) but I generally add tape anyway, just to be sure.
Everyone, Thanks for all the input.
The lawyer had called me in for work at his office, and then for the transfer switch. He had some recepts that didn't work (GFCI tripped) and another that didn't work that I ended up disconnecting on the load side (nail in cable?). Plus, the a ceiling fan cable must have been pierced because the light doesn't work, but the fan does.
To make a long story short, even after explaning (to a lawyer, no less!) that this house was new enough to still be under warranty, and all of this should be fixed free of charge, he looked me in the eye and said he'd rather pay me to fix it than have the "inspector" come back.
Wow!
Opinions and comments?