1 members (Scott35), 176 guests, and 12 robots.
spyder Offline OP
I know many manufacturers require GFCI protection for fixtures when used in Tub and Shower locations.
Does the NEC also have this requirement?
The NEC does not require GFCI protection of fixtures over tub or shower enclosures but if the fixture manufacture requires protection then you must provide it.
You say that many manufactures require GFCI protection? I have never seen this requirement on any fixtures other than fans.
Curt
Curt Swartz
spyder Offline OP
Curt,
Your right, now that I think about it, I have only seen it required by manufactures of bath fan and bath fan/lite combos.
If I'm not mistaken, Progress Recessed Canisters (P87-AT) and the Shower Trims (P8025-60) require GFCI protection for use in shower stalls.
-Virgil
5 Star Inspections
Member IAEI
Q~ how many take advantage of the EX to 210.11(C)(3) here vs. blank faced GFI's?
spyder Offline OP
Sparky,
I almost always provide GFCI protection in tub and shower enclosures for fixtures regardless of whether or not the manufacturer requires it. I do so most often using the execption you mention.
spyder,
me too.
those blank faced GFI's were a hard sell for me.