Is a residential everyday type dishwasher required to have a means of disconnect other than the branch circuit fuse or cicuit breaker?

Work Gear for Electricians and the Trades

Workgear for Electricians

#82036 10/14/02 09:10 PM
Joined: Oct 2000
Posts: 5,393
S
Member
welcome spyder,

the 'off' position of most domestic dishwashers will not accept LOTO , which is why i suspect some locale's require a s.p. countertop switch.

#82037 10/14/02 09:45 PM
Joined: Feb 2002
Posts: 2,233
H
Member
A lot of contractors in my area are now installing a receptacle under the sink.

#82038 10/15/02 07:11 AM
Joined: Oct 2000
Posts: 5,393
S
Member
harold,
i do this exclusively, many times running a 3-wire for a future (undecided) pig.

i think it's a better job

[Linked Image]

#82039 10/15/02 02:52 PM
Joined: Jul 2002
Posts: 680
W
Member
Why do you need to LOTO a dishwasher, can't one LOTO the breaker that runs the dishwasher?. I can't see not using a dedicated circuit for DW unless it was put in after the fact.

#82040 10/15/02 03:32 PM
Joined: Oct 2002
Posts: 210
S
spyder Offline OP
Member
I agree that it might be a better installation to put a recptacle under the sink, but does the NEC require it or another means of disconnect within site of the unit? And if so would a LOTO on the circuit breaker be a legal exception?

#82041 10/15/02 06:22 PM
Joined: Oct 2000
Posts: 5,393
S
Member
part III of 422 gets into this. I think the LOTO part comes from 422.31(B), not that the average home owner or DIY'er would carry any.

422.34 details the different occupancies

this here [Linked Image] me.....

Quote

422.34 Unit Switch(es) as Disconnecting Means.
A unit switch(es) with a marked-off position that is a part of an appliance and disconnects all ungrounded conductors shall be permitted as the disconnecting means required by this article where other means for disconnection are provided in the following types of occupancies.

Quote
(C) One-Family Dwellings. In one-family dwellings, the service disconnecting means shall be permitted to be the other disconnecting means.

i'm a tad stuck on the verbage here, inparticular the 'other disco means'.....

Work Gear for Electricians and the Trades

Workgear for Electricians

#82042 10/16/02 04:31 PM
Joined: Oct 2002
Posts: 210
S
spyder Offline OP
Member
Would an inspector have the right to red tag a job based on the NEC if the dishwasher was hooked up directly with means of disconnect other than the circuit breaker?