Around here, I've come to understand that 250.110 and especially 250.114 still apply to the loads connected to GFI protected 2-wire ungrounded branch circuits. 406.3(D)(3)provides for the wiring method shown in the photo above, but when I bring in, say, a desktop computer with its grounded power supply cord, 250.114 says I still have to get the EGC connected to the power supply cord.