0 members (), 164 guests, and 10 robots.
Page 4 of 4 1 2 3 4
#81374 09/01/02 01:57 PM
One of the positive things about a min/max state is that they have a state appeals board. Since the state appeals board hears nothing but appeals from local boards and you can argue the appeal yourself as a licensee the local boards quickly become reluctant to appear incompetent to the state board. This eliminates the tin pot god syndrome that can develop in one and two person inspection offices.
[This message has been edited by tdhorne (edited 09-01-2002).]
Tom Horne
Workgear for Electricians
#81375 09/06/02 01:25 AM
Was the sub panel in a building attached to the main house or detached? Was there a ufer ground at the sub panel?
#81376 09/12/02 11:38 PM
To the point: two issues are raised.
First, there needs to be a fourth (ground) wire connecting the main panel with the sub-panel.
Second, the code conflicts here with common useage. The "main disconnect" breaker in a panel is not the same as what the code calls a "main disconnect." The NEC 'main disconnect" refers to the point where the utility lines ("main service") arrive at the meters. There can be no more than six meters without there being a single handle to disconnect all of them.
Everything after the meter is either a "feeder" to a sub-panel, or a "branch circuit." A sub-panel must have a disconnecting means, but this need not be at the sub-panel (it can be at the source panel). Under certain circumstances (called "tap rules") the overload protection need not be at the source.
As you can see, a journeyman is paid for his training, experience, and judgement- as well as his time. You've got to respect him for that.
Page 4 of 4 1 2 3 4