NEC Article 430 #81248
07/29/02 03:48 PM
07/29/02 03:48 PM
O
ongmark  Offline OP
Junior Member
Joined: Jul 2002
Posts: 2
Salem, OR, USA
Minimum size branch circuit for (1) 15HP, 208v, 3phase, design letter "B", operating at 80% power factor.
I know the process, however the design letter and PF are throwing me?

Any help would be greatly appreciated.

2017 / 2014 NEC & Related Books and Study Guides
Re: NEC Article 430 #81249
07/29/02 04:03 PM
07/29/02 04:03 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,347
ongmark,
do you actually have a 'B'motor?

[This message has been edited by sparky (edited 07-29-2002).]

Re: NEC Article 430 #81250
07/29/02 05:02 PM
07/29/02 05:02 PM
O
ongmark  Offline OP
Junior Member
Joined: Jul 2002
Posts: 2
Salem, OR, USA
Yes

Re: NEC Article 430 #81251
07/29/02 05:59 PM
07/29/02 05:59 PM
3
3 Way  Offline
Junior Member
Joined: Jul 2002
Posts: 6
TX
ongmark,

for one motor on the branch...
size branch circuit @ 125% of motor full load amps as listed in NEC 430.150.
15HP @ 208V 3ph ==> 46.2 amps
125% ==> 57.8 amps
select wire (after derations) for 57.8 amps

the design letter "B" is used for selecting overload protection
PF=80% is typical for induction motors but has no bearing on wire size. NEC table 430.150 has PF allowances "built-in" for induction motors.

hope this helps.

Re: NEC Article 430 #81252
08/08/02 03:26 PM
08/08/02 03:26 PM
D
Dan Neeser  Offline
Member
Joined: Mar 2002
Posts: 29
St. Louis, MO, USA
I think your question has been answered, but just an fyi.

A good reference tool that we provide is in the Bussmann SPD. See 84-99 for the Motor Circuit Table that shows the sizing required. The link for the SPD is below, below that is the link for other pubs and articles.
http://www.bussmann.com/library/docs/Spd.pdf http://www.bussmann.com/apen/pubs/


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,084 Are you busy
181,127 Re: Forum
171,323 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.9660 MB (Peak: 1.1048 MB) Zlib enabled. Server Time: 2018-02-25 17:58:18 UTC