ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Ground Rods: Installation and Hook-Up
by renosteinke - 11/29/22 07:43 PM
Colt Firearms Switchbox
by NORCAL - 11/29/22 01:04 AM
Happy Thanksgiving all!
by Bill Addiss - 11/24/22 08:37 AM
Perfect work light?
by gfretwell - 11/22/22 12:48 AM
copper prices where you live and inflation
by gfretwell - 11/21/22 01:52 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 46 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#80909 06/10/02 05:07 PM
Joined: Jan 2002
Posts: 64
R
Rabbit Offline OP
Member
Am coming out of the main switch gear in a hospital with a 480v 150a feed. The gear is in the basement. This will feed a new 208/120 panel on the 3rd floor via a transformer, also on the 3rd floor. The print shows the feeder going strait to the trans. Don't I need a disconnect here? Panel is main brkr. Also this panel will serve some isolated ground circuits. Does the ig have to go all the way back to the gear or can it stop at the trans? Articals?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#80910 06/10/02 05:36 PM
Joined: Nov 2000
Posts: 2,148
R
Member
There is not a code requirement to have a disconnect at the transformer. The transformer primary does require an OCPD, but that can be at the main gear and provide the required protection for both the feeder conductors and the primary side of the transformer. As for your isolated grounds look at 250.146(D). They must trerminate at a point where they can clear any ground fault. For your SDS, that would be at the same point where you connect the grounding electrode conductor for the secondary of the transformer.
Don

[This message has been edited by resqcapt19 (edited 06-10-2002).]


Don(resqcapt19)
#80911 06/10/02 07:39 PM
Joined: Sep 2001
Posts: 25
D
Member
I would think that a disconnect would be required to protect the secondary conductors.
240-21(c)(1) seems to indicate that the secondary conductors are not protected by the primary OCPD, and I am not sure that I would like unprotected conductors running 3 floor til they get to the mail in the load center.

#80912 06/10/02 08:39 PM
Joined: Jan 2002
Posts: 64
R
Rabbit Offline OP
Member
Thanks Don. This is my first hospital and it just didn,t look right. I will proceed.
Dlabrenz, the conductors are protected at the switch gear, approx. 150 ft.

#80913 06/10/02 09:39 PM
Joined: Nov 2000
Posts: 2,148
R
Member
dlabrenz,
The main in the panel can provide the required protection of the secondary side of the transformer and the secondary conductors. This may involve the use of the "tap" rules that will limit the length of the secondary conductors.
Don


Don(resqcapt19)

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
NORCAL 5
Trumpy 3
Popular Topics(Views)
300,319 Are you busy
229,993 Re: Forum
214,806 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5