Geen Wire is Not Used as an Equipment Grounding Conductor? #80855
06/07/02 06:20 PM
06/07/02 06:20 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
"GENERAL

This category covers cable investigated in accordance with International Municipal Signal Association Inc. specifications.

The cable is intended for installation as aerial cable or in underground conduit as part of a traffic signal system.

This cable employs a color-code scheme that permits a conductor with green insulation to be used for other than grounding purposes.

These cables have not been evaluated for flammability.

This cable is not suitable for use as a substitute for cable or wiring systems covered in NFPA 70, "National Electrical Code."

QUESTIONS: Why? Do these systems fall within the scope of Article 725?



[This message has been edited by Joe Tedesco (edited 06-07-2002).]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Geen Wire is Not Used as an Equipment Grounding Conductor? #80856
06/07/02 08:41 PM
06/07/02 08:41 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
What would you bet that "green" was needed for lights of the same? Blue would have brought the system into meltdown.

At one time plain-vanilla tray and pendant cables used green and white in various combinations for conductor identification. The allowance for leaving out green and white in multiconductor assemblies is about 12 years old.

“NEMA WC57-1995/ICEA S-73-532” Table E2 (formerly K2) leaves out green and white from the list. Example at: http://www.nexans.ca/egy/equip/ultx_tc/tray22.htm http://www.drakausa.com/pdfsTAM/t10TPV.pdf http://www.sns.gov/projectinfo/ics/...0Information/Technical%20Information.pdf page 35 has both “K1” and “K2” charts.

Re: Geen Wire is Not Used as an Equipment Grounding Conductor? #80857
06/07/02 09:16 PM
06/07/02 09:16 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Bjarney:

Thanks! This information is very helpful. I was always concerned about the use of the cable I described above listed by UL.


Joe Tedesco, NEC Consultant
Re: Geen Wire is Not Used as an Equipment Grounding Conductor? #80858
06/07/02 11:44 PM
06/07/02 11:44 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
If I follow the code correctly, nowadays you can reidentify individual conductors as equipment grounds or grounded circuit conductors in a multiconductor cable, but not the reverse. If one could not use white or green for other than these under the “old” scheme, {although 600V-rated} you’d end up with lots of worthless “spares.”

Re: Geen Wire is Not Used as an Equipment Grounding Conductor? #80859
07/02/02 12:00 AM
07/02/02 12:00 AM
T
Tom Baker  Offline
Member
Joined: Oct 2001
Posts: 30
Bremerton WA
Joe, this cable is commonly used by the Traffic Signal industry, and is called IMSA 19-1 (International Municpial Siganl Association, 19-1 is the cable spec).

It is a five conductor cable
White-common
Red-red display
Yelllow-yellow display
Green-green display
Black-spare, sometimes used in ped signals

Signal heads typically don't have a seperate equipment groudning conductor, but the mast arms are often connected to an EGD.

Many companies make a 19-1 cable, but I don't think a much of it is listed. I'm going to check on this. In fact very, very, little traffic signal equipment is listed. This causes problems with installations where the AHJ gets involved.

I'm a certified Traffic Signal Tech and have been writing a "Code Corner" column in the IMSA Journal for the 18 months.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,862 Are you busy
184,214 Re: Forum
173,456 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.006s) Memory: 0.9705 MB (Peak: 1.1053 MB) Zlib enabled. Server Time: 2018-05-22 11:45:25 UTC