Delta Skelter #80848
06/07/02 03:41 PM
06/07/02 03:41 PM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,351
I am stumped here. There is a 3 ph 4 wire panel, voltages to G are 120,120,240.
There re only two X-formers on the pole, the bracket is visible where the third can may have been....

2017 / 2014 NEC & Related Books and Study Guides
Re: Delta Skelter #80849
06/07/02 04:30 PM
06/07/02 04:30 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Sparky,
Sounds like an open delta with a wild leg, but the 240 to g should be closer to 208.
Don


Don(resqcapt19)
Re: Delta Skelter #80850
06/07/02 04:43 PM
06/07/02 04:43 PM
A
ameterguy  Offline
Member
Joined: May 2002
Posts: 30
Mass
Sparky,

I agree with Don, delta, with center tap. Usually you should get:
a - g 120
b- g 120
c - g 208

a- b 240
a- c 240
b- b 240

What are your phase to phase voltage readings?

Re: Delta Skelter #80851
06/07/02 06:36 PM
06/07/02 06:36 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.

Re: Delta Skelter #80852
06/08/02 07:21 AM
06/08/02 07:21 AM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,351
ameterguy,
the readings are as you've stated.sorry 'bout that...
( 'twas a dark rainy night, etc, etc..) The high leg is marked white, removing the panel cover is like taking the bra off the fat lady....


Roger, yep that's the beast.. is the grounding conductor common to the primary??
[Linked Image]
[Linked Image]

Re: Delta Skelter #80853
06/08/02 08:36 AM
06/08/02 08:36 AM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Sparky, The grounding conductor could be common to both. The real caution here would be lets say you were going to make this installation verses the utility. If your primary were an ungrounded delta and you were going to provide a grounded system, the grounding would have to be isolated on the secondary side.

Roger

Re: Delta Skelter #80854
06/08/02 10:34 AM
06/08/02 10:34 AM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
There one more variation of the open-delta arrangement used by electric utilities, and fairly common in some areas—that is open-wye grounded primary, open-delta secondary. At: http://www.elec-toolbox.com/usefulinfo/xfmr-3ph.htm you can visualize it looking at Fig.1-1 Y-∆ layout. Now remove the primary winding at the ten o’clock position that is connected to L2. The hi-side wye point has to be connected to the hi-side neutral conductor [not shown on 1-1.] so there are still three conductors serving on the primary side of the bank. Now, on the secondary, delete the winding at the 2 o’clock position. [Sometimes this is incorrectly called ‘two-phase,’ but that designation is reserved specifically for 90° phase-displaced voltages.]

In areas where the multigrounded common neutral is used, it saves a fused cutout and wire for the unneeded third phase. {For geeks only—In some areas where lo-side delta voltages are needed, a grounded wye-delta bank is prohibited, for it acts as an undesirable ground source and can induce high currents in the common-neutral conductor during hi-side faults.}


[This message has been edited by Bjarney (edited 06-08-2002).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,669 Are you busy
186,403 Re: Forum
175,893 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.006s) Memory: 0.9851 MB (Peak: 1.1380 MB) Zlib enabled. Server Time: 2018-08-21 08:00:37 UTC