#80485 04/19/02 11:13 PM
Joined: Jan 2002
Posts: 31
D
Member
where in the 2002 code book can i find my ans. we need to put in five 200 amp services on a commercial building. five stores (strip). what size does the feeder need to be? itis coming off a tranformer next to the building. no markings on the transformer. i think they should be five 100 amp panels. the store is not that big, 25'x 60'. also can the feeders run along the side of the building, close to the top. my co-worker says yes. then we would tap off of 5 times. need help, thanks guys.

dan

Horizontal Ad
#80486 04/20/02 12:29 AM
Joined: Dec 2001
Posts: 440
Likes: 3
Member
In my opinion, you need to know what the load on each tent space is going to be.
Are they continuous, noncontiuous, motor loads, how much lighting, and what type, etc, etc, etc?
As it looks right now, you are about to build a 1000 amp service for a building that may not need half of that.
Try Parts I & II of article 220.

Regards,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
#80487 04/20/02 08:12 AM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Daniel,

Are you running feeders or are these service entrances? If this is not a service entrance, you'll need over current protection close to the transformer to protect the feeder.

Like Doc said, do the calculations, SWAGS aren't allowed in this case.

Tom


Few things are harder to put up with than the annoyance of a good example.
#80488 04/20/02 11:28 AM
Joined: Apr 2001
Posts: 507
G
Member
"Try Parts I & II of article 220.
Regards,
Doc"

REGARDS!! Come on Doc, what's up with regards? Your fans have high expectations when we see your posts.....you can't let us down with a simple regards. [Linked Image]

GJ

#80489 04/20/02 10:39 PM
Joined: Jan 2002
Posts: 31
D
Member
the owner of the place wanted 200 amp for each store. my boss told him he may not need that. he said that is what he wanted. i agree with what you are saying doc. tom these are service entrance, i think. the are coming from the tranformer. would that be feeders then? hey thanks for the help guys. also, is it ok to run the cables from the tranformer along the building, then tap off for each service?


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
329,934 Are you busy
254,767 Re: Forum
237,186 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5