ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Unusual Well Pump Switch Failure
by sabrown - 10/28/20 04:31 PM
Look at this mess...
by InspectorE - 10/27/20 09:09 PM
New tool
by gfretwell - 10/24/20 11:09 AM
Where is Everyone?
by Bill Addiss - 10/17/20 07:04 PM
New in the Gallery:
Facebook follies, bad wiring
FPE in Germany pt.2
Who's Online Now
0 registered members (), 14 guests, and 17 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Derating and Maximum # of Conductors #80427 04/11/02 12:59 PM
Joined: Oct 2000
Posts: 3,631
Admin Offline OP
Administrator
Member
Quote
Would you help us resolve a question of derating and maximum number of conductors in a raceway?

Please refer to the 2002 NEC Handbook for the following question:

We are discussing how to properly derate conductors in raceway when the quantity of conductors exceeds 85.

The wiring application in question is for theaters and involves stage, concert and house lighting circuits controlled by solid state dimming racks. Many dimming racks in large theaters have 90 or more dimmer modules resulting in at least 180 current carrying conductors plus ground conductors. Metal wireway is often used to route conductors from the dimmer racks to the fixtures. The wireway is sized for the maximum 20 percent fill required by Article 376. We are applying Article 520.6 that grants exception to the 30 conductor maximum rule in Article 376.

The question of properly derating remains. Note: Load diversity is often 50% or greater.

Table B.310.11 appears to apply. The problem is that this table does not seem to address more than 85 conductors. The FPN following the table refers to "special calculations required" but does not specify further reading or guidelines to perform the calculations.

Jeffrey M. Leavenworth, P.E.

2017 / 2014 NEC & Related Books and Study Guides
Re: Derating and Maximum # of Conductors #80428 04/11/02 11:53 PM
Joined: Oct 2000
Posts: 2,721
Scott35 Online Happy
Broom Pusher and
Member
My NEC [1999] is in the Van and it's getting late, but I would like to address this message, so I'll toss some numbers and stuff in this thread later.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Derating and Maximum # of Conductors #80429 04/13/02 01:39 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Jeff,
I do not have the 2002 code yet but the
99 code section 318-11 seems to apply to your installation.

Re: Derating and Maximum # of Conductors #80430 04/15/02 01:28 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
This query has been lying here festering for a couple of days. Seems like no one really wants to get out in the lead (and become a target).

Here goes. If you are applying 520.6, and are otherwise in compliance with that article, no derating of the conductors is required.

The last sentence waives the 30 conductor limitation of 366.6 & 376.22 Both of these require derating when exceeding 30 current carrying conductors. Since the rule is waived, derating is not required.

Do I need to put on my asbestos coveralls?

[This message has been edited by Tom (edited 04-15-2002).]


Few things are harder to put up with than the annoyance of a good example.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,051 Are you busy
205,040 Re: Forum
193,164 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3