Main Panel in Bathroom #80269
03/27/02 05:06 PM
03/27/02 05:06 PM
T
troythom  Offline OP
Junior Member
Joined: Mar 2002
Posts: 3
Kentland, IN USA
Greetings,

First time posting but have learned much from reading.

Is it allowable to have the main breaker panel in a bathroom/laundry room area? If so, what are the rules that apply?

Thanks in advance...

2017 / 2014 NEC & Related Books and Study Guides
Re: Main Panel in Bathroom #80270
03/27/02 06:36 PM
03/27/02 06:36 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Welcome to the forum.

No, No 1000X no. [Linked Image]

240.24(E)

MAke sure that this room is in fact a bathroom by seeing the NEC definition of a bathroom in article 100.

Some of the rules that apply can be found in Article 240 (Overcurrent Devices), Article 312 Cabinets & Cutout boxes (this is the box that the panelboard is installed in), Article 408 Switchboards & Panelboards, Article 110 Requirements for electrical installations, plus much more.

Tom

[This message has been edited by Tom (edited 03-27-2002).]

[This message has been edited by Tom (edited 03-27-2002).]


Few things are harder to put up with than the annoyance of a good example.
Re: Main Panel in Bathroom #80271
03/27/02 07:16 PM
03/27/02 07:16 PM
T
troythom  Offline OP
Junior Member
Joined: Mar 2002
Posts: 3
Kentland, IN USA
Thanks for the info. In this case it is in fact a bathroom.

What about if it was just a laundry room? No vanity, toilet, or shower/tub but just a washer/dryer connection?

Re: Main Panel in Bathroom #80272
03/27/02 07:51 PM
03/27/02 07:51 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
troythom;
greetings.

a 'laundry ' room, as you describe, would be ok, just maintain proper clearance around the panelboard......

[Linked Image]

Re: Main Panel in Bathroom #80273
03/28/02 07:37 AM
03/28/02 07:37 AM
T
troythom  Offline OP
Junior Member
Joined: Mar 2002
Posts: 3
Kentland, IN USA
Thanks all!

Re: Main Panel in Bathroom #80274
03/28/02 07:37 PM
03/28/02 07:37 PM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
OK, how about this one.

Sub-panel, commercial building, in a bathroom within reach of a sink and toilet?

GJ

Re: Main Panel in Bathroom #80275
03/28/02 08:19 PM
03/28/02 08:19 PM
C
circuit man  Offline
Member
Joined: Nov 2001
Posts: 273
saluda,s.c.
not a pleasent thought golf junkie.:eek;

Re: Main Panel in Bathroom #80276
03/29/02 10:59 AM
03/29/02 10:59 AM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
A sub-panel would be allowed, as far as I can tell, since it does not contain the service disconnecting means (230.70(A)(2))& is not one of the prohibited bathrooms in 240.24(E).

Evidently, people are inherently safer when they are in a non-residential type setting. [Linked Image]


Few things are harder to put up with than the annoyance of a good example.
Re: Main Panel in Bathroom #80277
03/29/02 11:28 AM
03/29/02 11:28 AM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
"Evidently, people are inherently safer when they are in a non-residential type setting."

Yep...
This was on a major remodel of a county courthouse. The job was engineered....so who am I to question? ......apparently this was done to keep the panel out of view.

It passed inspection without question.

GJ

OK tom, how do you do the roll smilie? I've tried and all i get is :roll:

[This message has been edited by golf junkie (edited 03-29-2002).]

[This message has been edited by golf junkie (edited 03-29-2002).]

[This message has been edited by golf junkie (edited 03-29-2002).]

Re: Main Panel in Bathroom #80278
03/29/02 08:10 PM
03/29/02 08:10 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Golf Junkie,
Glad the inspector passed the installation. Evidently, he couldn't find anyrhing in the NEC either, that would prohibit a subpanel in a commercial/institutional/industrial bathroom.

The rolleyes is plural, usually can't remember what to type so I just copy & paste from the smilies legend which is accessible when you're typing a reply.

Tom

[This message has been edited by Tom (edited 03-29-2002).]


Few things are harder to put up with than the annoyance of a good example.
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
djk 2
Popular Topics(Views)
251,541 Are you busy
188,707 Re: Forum
178,412 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 1.0247 MB (Peak: 1.2017 MB) Zlib enabled. Server Time: 2018-11-17 21:28:54 UTC