ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Where is Everyone?
by luckyshadow - 11/21/21 10:14 AM
It's been an interesting career
by The Watt Doctor - 11/19/21 09:56 AM
Well I am back to stay (nearly 6 years)
by The Watt Doctor - 11/19/21 09:17 AM
Motor Load Relationships Between Fans and Pumps
by The Watt Doctor - 11/18/21 09:24 AM
GFCI's pops in large numbers
by dsk - 11/05/21 06:45 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 24 guests, and 22 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#80269 03/27/02 05:06 PM
Joined: Mar 2002
Posts: 3
T
Junior Member
Greetings,

First time posting but have learned much from reading.

Is it allowable to have the main breaker panel in a bathroom/laundry room area? If so, what are the rules that apply?

Thanks in advance...

2017 / 2014 NEC & Related Books and Study Guides
#80270 03/27/02 06:36 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Welcome to the forum.

No, No 1000X no. [Linked Image]

240.24(E)

MAke sure that this room is in fact a bathroom by seeing the NEC definition of a bathroom in article 100.

Some of the rules that apply can be found in Article 240 (Overcurrent Devices), Article 312 Cabinets & Cutout boxes (this is the box that the panelboard is installed in), Article 408 Switchboards & Panelboards, Article 110 Requirements for electrical installations, plus much more.

Tom

[This message has been edited by Tom (edited 03-27-2002).]

[This message has been edited by Tom (edited 03-27-2002).]


Few things are harder to put up with than the annoyance of a good example.
#80271 03/27/02 07:16 PM
Joined: Mar 2002
Posts: 3
T
Junior Member
Thanks for the info. In this case it is in fact a bathroom.

What about if it was just a laundry room? No vanity, toilet, or shower/tub but just a washer/dryer connection?

#80272 03/27/02 07:51 PM
Joined: Oct 2000
Posts: 5,389
S
Member
troythom;
greetings.

a 'laundry ' room, as you describe, would be ok, just maintain proper clearance around the panelboard......

[Linked Image]

#80273 03/28/02 07:37 AM
Joined: Mar 2002
Posts: 3
T
Junior Member
Thanks all!

#80274 03/28/02 07:37 PM
Joined: Apr 2001
Posts: 507
G
Member
OK, how about this one.

Sub-panel, commercial building, in a bathroom within reach of a sink and toilet?

GJ

#80275 03/28/02 08:19 PM
Joined: Nov 2001
Posts: 273
C
Member
not a pleasent thought golf junkie.:eek;

#80276 03/29/02 10:59 AM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
A sub-panel would be allowed, as far as I can tell, since it does not contain the service disconnecting means (230.70(A)(2))& is not one of the prohibited bathrooms in 240.24(E).

Evidently, people are inherently safer when they are in a non-residential type setting. [Linked Image]


Few things are harder to put up with than the annoyance of a good example.
#80277 03/29/02 11:28 AM
Joined: Apr 2001
Posts: 507
G
Member
"Evidently, people are inherently safer when they are in a non-residential type setting."

Yep...
This was on a major remodel of a county courthouse. The job was engineered....so who am I to question? ......apparently this was done to keep the panel out of view.

It passed inspection without question.

GJ

OK tom, how do you do the roll smilie? I've tried and all i get is :roll:

[This message has been edited by golf junkie (edited 03-29-2002).]

[This message has been edited by golf junkie (edited 03-29-2002).]

[This message has been edited by golf junkie (edited 03-29-2002).]

#80278 03/29/02 08:10 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Golf Junkie,
Glad the inspector passed the installation. Evidently, he couldn't find anyrhing in the NEC either, that would prohibit a subpanel in a commercial/institutional/industrial bathroom.

The rolleyes is plural, usually can't remember what to type so I just copy & paste from the smilies legend which is accessible when you're typing a reply.

Tom

[This message has been edited by Tom (edited 03-29-2002).]


Few things are harder to put up with than the annoyance of a good example.
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 28
Joined: June 2004
Top Posters(30 Days)
Trumpy 5
dsk 3
Popular Topics(Views)
286,157 Are you busy
218,583 Re: Forum
204,800 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5