Grounding to water pipe #80011 02/13/02 11:31 PM
Joined: Feb 2002
Posts: 22
B
beach Offline OP
Member
A licensed electrical contractor I work with says running a ground wire from a recpt to a water pipe bonding with a copper strap is an approved method for obtaining a ground from a 2 wire system. Example: knob and tube wiring, he ran a #12 wire from the recpt to a water pipe (3/4 galv) to acheive a ground. I argued with him since it was my belief this was not an approved method.

Please shed some light please. I have a 2002 NEC. Please reference some code so I can better understand, also a suggested approved method if his is not.

The local is Sacramento, CA In city limits.

Thank you
Jon

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding to water pipe #80012 02/13/02 11:39 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Jon,
Look at 250.130(C)
Don(rescqpt19)


Don(resqcapt19)
Re: Grounding to water pipe #80013 02/14/02 12:03 AM
Joined: Feb 2002
Posts: 22
B
beach Offline OP
Member
In reading it is my understanding that his connection is only permitted if within 5 ft of the pipe entrance since it is not a commercial or indusrtial but rather a residential building.

IS THIS CORRECT?

Jon

Re: Grounding to water pipe #80014 02/14/02 06:37 AM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
beach,
first you must consider if said conductor is a 'Bond" or a 'Grounding Electrode Conductor' (or GEC). The 5' rule would apply to the latter.

Re: Grounding to water pipe #80015 02/14/02 08:34 AM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
Jon, I believe you are correct, you must run the ground to within 5 feet of water line point of entry, or you could run it into the panels ground bar. This or may not be accepted where you are. Here in Mass we are not allowed to do this. They have deleted 250.130(C)

Re: Grounding to water pipe #80016 02/14/02 06:45 PM
Joined: Jan 2002
Posts: 163
D
dana1028 Offline
Member
Beach - you are in Calif. - the NEC 1996 is the state adopted code (not '99 or 2002) -...so

250-50(b)Excetion - says "shall be permitted to be grounded to any accessible point on the GES as described in 250-81, or to any accessible point on the GEC."...going to 250-81....
250-81(a) - Metal underground water pipe - there is no requirement for attaching within 5' of entry into the bldg....(unless I missed somthing but I don't think I did) ....so - your elect. contractor wired this correctly....until Calif. finally gets around to adopting the 1999.

Re: Grounding to water pipe #80017 02/14/02 07:44 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
Wow I can not beleive there are states out there that do not keep up with current code. Anyone still using the knob and tube out there?

Re: Grounding to water pipe #80018 02/15/02 01:27 AM
Joined: Feb 2002
Posts: 22
B
beach Offline OP
Member
Knob and tube? Of course....Why? Have you heard of something better?

Re: Grounding to water pipe #80019 02/15/02 01:39 AM
Joined: Sep 2001
Posts: 25
D
dlabrenz Offline
Member
The 5 foot rule for the water pipe connection first appeared in the 1993 NEC. If the grounding connection was not made within the first five feet from the point where the water service enters the building, it would not appear to be done correctly.

Re: Grounding to water pipe #80020 02/15/02 09:09 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
Knob and tube is still an acceptable wiring method as an extension to existing k&t.
Not that I would choose to do so.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,928 Are you busy
204,357 Re: Forum
192,574 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3