I will be installing electric baseboard heat in an attic/playroom conversion. 3 sections for 4500 watts (which equals 18.75 amps @ 240 v.)
424.3(B) requires 125% for branch circuit conductors and OCPDs. This comes to 23.4 amps. I plan to run a 30 amp circuit and I want to install a line voltage t-stat as opposed to low voltage relaying.
The problem is I can't locate a t-stat rated above 22 amps. This will handle the 18.75 amp load but I'm not sure if the t-stat is also required to be rated @ 125%. (23.4 amps)
Help, anyone?

Horizontal Ad
#80010 02/13/02 03:38 PM
Joined: Dec 2001
Posts: 270
E
Member
I would treat the t-stat like any other switch. See 380-14(a). The 22Amp t-stat is good for the 18.75Amp load. The wiring is sized no more than 80% so there will not be any heat buildup at the terminal screws, and there is no service factor, like in motors, to worry about with the resistive load.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
Popular Topics(Views)
333,593 Are you busy
258,964 Re: Forum
240,394 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5