#79996 02/12/02 08:35 PM
Joined: Jul 2001
Posts: 29
T
tmon Offline OP
Member
Does a 2 pole gfci circuit breaker compare the two ungrounded conductors ampacities like a single pole compares the hot and neutral? I am wondering if I can use it on a masonry saw that does not utilize a neutral conductor and still be protected. Thanks

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2000
Posts: 2,148
R
Member
It compares the 2 hots if it is a 240 GFCI and compares a three wires if it is a 120/240 GFCI. Either one will provide protection for a 240 volt saw.
Don(resqcapt19)