2 pole GFCI circuit breaker #79996 02/12/02 08:35 PM
Joined: Jul 2001
Posts: 29
T
tmon Offline OP
Member
Does a 2 pole gfci circuit breaker compare the two ungrounded conductors ampacities like a single pole compares the hot and neutral? I am wondering if I can use it on a masonry saw that does not utilize a neutral conductor and still be protected. Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: 2 pole GFCI circuit breaker #79997 02/12/02 09:07 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
It compares the 2 hots if it is a 240 GFCI and compares a three wires if it is a 120/240 GFCI. Either one will provide protection for a 240 volt saw.
Don(resqcapt19)


Don(resqcapt19)

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,069 Are you busy
205,048 Re: Forum
193,177 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3