Overkill? #79965
02/11/02 01:32 AM
02/11/02 01:32 AM
N
NoShorts4Me  Offline OP
Member
Joined: Jan 2002
Posts: 36
southern california
I'd appreciate some feed back on this.
Friend of mine owns a custom racemotor shop.He recently bought what I think he called a "shore-pac" unit. Basically a rolling unit with a 480v 3-phase motor ( 8 amps) which drives a large fan for ventilation, for use when welding certain metals. (some osha requirement). The unit would need to be rolled around the shop close to wherever the welding was done.The 480v service panel is located in his shop, but you must exit is shop and walk around the other side of the building for access.All he wanted was advice as to what to suggest to or expect from the E.C. he hired.
My suggestions off the top of my head was..
-3/4" emt (approx.75') w/3- #10's+ grounding conductor on a 15 amp breaker.

- a 30 amp fusible disconnect with integral twistlock plug where the plug can not be removed with out de-energizing the load side of the disconnect. ( I believe Hubbel makes these...."circuit-locks" ??)

-50' of 8-3 w/g cord with the proper Pin/Sleeve connectors ( not sold on this with 480, but I couldnt come up with a safer way considering the mobility need)

- strain reliefs on the cord at the disconnect location and "shore-pac", to hold the cord secure.

Now, what WAS installed a week later ( by a NATIONAL known electrical contractor) ..

- 75' of 1/2" emt with 3-# 12's ( no ground)
- a 480v twistlock plug ( not pin/sleeve) in a 5-square box with raised cover.

DONE!

Was I way of base with this? (overkill) ???

At the very LEAST a disconnect.
Sorry for being so long winded.

Regards,
NS4M

2017 / 2014 NEC & Related Books and Study Guides
Re: Overkill? #79966
02/11/02 08:41 AM
02/11/02 08:41 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
A few thoughts--
Does the unit have a starter or combination starter on it? Although the plug may qualify as a disconnect for the motor, a switch would be nice. In an emergency, I would not want to unplug it under load.
The 3 #12s don't seem to be a problem, but at 480 volts, an EGC would certainly provide a much safer installation.
Also, depending on the size of the shop, more than one receptacle would be nice. This would minimize cord length, and the likelihood of it being damaged.

Re: Overkill? #79967
02/11/02 03:42 PM
02/11/02 03:42 PM
B
bob3232  Offline
Junior Member
Joined: Feb 2002
Posts: 4
It sounds like this is a 5 hp motor.If it is you have to size the conductor for about 9.5 or 10 amps.With motors you can use the amperage from table 310-16 A #12thhn is good for 30 amps.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Popular Topics(Views)
249,457 Are you busy
187,376 Re: Forum
176,719 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.033s Queries: 14 (0.013s) Memory: 0.9512 MB (Peak: 1.0755 MB) Zlib enabled. Server Time: 2018-09-25 17:40:24 UTC