ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Solar PV Wiring Errors
by renosteinke - 03/02/24 08:12 PM
Do You Wrap Your Receptacles?
by gfretwell - 02/20/24 10:48 PM
Cable Chase Code Requirement
by renosteinke - 02/16/24 07:00 PM
Do we need grounding?
by gfretwell - 02/16/24 10:37 AM
Cordless Tools: The Obvious Question
by gfretwell - 02/08/24 07:28 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 23 guests, and 32 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#79709 01/13/02 05:04 PM
Joined: Jan 2002
Posts: 1,457
E
Member
Can anyone tell me where to find code info on sizing appliance cords? I can not seem to find anything regarding dishwashers in particular. Seems most electrical appliances come with cords rated for less than a 15 or 20 amp circuit. I would like a definitive answer on installing a cord on a dishwasher. Thanks....Scott

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#79710 01/13/02 10:34 PM
Joined: Dec 2001
Posts: 270
E
Member
Some of the info can be found in 422-16(b)(2). Length 3' to 4' from grounding type plug on cord to rear of appliance.
Then check out 240-4 for wire size and OC protection relative to what the nameplate of your dishwasher says. Probably SP type cord (table 400-4) 14 or 12 AWG. You really need to check out the local code because this is a subject frequently visited and amended by state and local authorities.

#79711 01/14/02 04:57 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
In general, ampacities of most common types of flexible cord can be found in Table 400-5(A) You can usually use Column B, but check out the small print at the bottom of the table.

Here's an example, 2 burner hot plate draws 20 amps, needs to be on a 30 amp breaker since it will be on all day. Branch circuit conductors are #10, but the cord only needs to be a maximum of #12.


Few things are harder to put up with than the annoyance of a good example.