725.52(A) Ex. #2 #79453
12/27/01 09:27 PM
12/27/01 09:27 PM
R
resqcapt19  Offline OP
Member
Joined: Nov 2000
Posts: 2,148
IL
What does this new exception mean? Does it throw out 725.55?
Don(resqcapt19)


Don(resqcapt19)
2017 / 2014 NEC & Related Books and Study Guides
Re: 725.52(A) Ex. #2 #79454
12/28/01 07:53 AM
12/28/01 07:53 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,278
Fullerton, CA USA
Being that the circuit is reclassified as a Class 1 circuit, it sure does look like it would invalidate 725.55

Re: 725.52(A) Ex. #2 #79455
12/31/01 11:11 PM
12/31/01 11:11 PM
E
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
This is an interesting change. I was taught to think that ONE reason for all the efforts to separate class 2 and 3 wiring from class 1 and power wiring was to protect the technician who thinks he is only dealing with 24 volts from inadvertently getting nailed with higher voltages. I guess this change pretty much nullifies that notion. All they must be concerned with is fire, induction, and fire/smoke characteristics of unprotected cabling!

Re: 725.52(A) Ex. #2 #79456
01/01/02 10:31 AM
01/01/02 10:31 AM
G
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
How can a Class 2 system which was installed by using Class 2 wiring become a Class 1 system just by removing the Class 2 marking on the system?

Would not the system need to be re-wired using 600 volt wiring and Chapter 3 wiring methods as per 725.27(B) ?

Re: 725.52(A) Ex. #2 #79457
01/01/02 10:51 AM
01/01/02 10:51 AM
R
resqcapt19  Offline OP
Member
Joined: Nov 2000
Posts: 2,148
IL
Just changing the the wiring method doesn't make a Class 2 system a Class 1 system. I realy have no idea what CMP 16 was trying to do here. If this is applied in the way that it reads, it does away with 725.55 and I don't think that is the intent.
Don(resqcapt19)


Don(resqcapt19)
Re: 725.52(A) Ex. #2 #79458
01/01/02 10:52 AM
01/01/02 10:52 AM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Glenn,

I think the key phrase in this is "installed as Class 1 circuits." This, as you point out, would require the use of an article 300 wiring method.

I can't imagine why someone would want to just go out & change & existing Class 2 or 3 installation, but there are plenty of times in new work where going to Class 1 makes sense.

This issue was posed at an IAEI chapter meeting several years ago (can't remember which chapter & when) & the response was split about evenly.

If the entire installation complies with Class 1 wiring requirements with an article 300 wiring method, I don't see the hazard that would be introduced. When I see an article 300 wiring method, I presume I'm dealing with at least 120 volts. On the other hand, I have seen lighting outlets wired with doorbell wire and telephone wire. What a surprise that would have been for someone if they cut the cable!

Don, sometimes I think the new code books should come with a deck of Tarot cards.

Tom

[This message has been edited by Tom (edited 01-01-2002).]


Few things are harder to put up with than the annoyance of a good example.
Re: 725.52(A) Ex. #2 #79459
01/01/02 11:26 AM
01/01/02 11:26 AM
G
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
Maybe the 725.52(A) text and the FPN text should just remove words " reclassified and ".

Now the circuit is being installed as a Class 1 .


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
BigB 3
Popular Topics(Views)
252,788 Are you busy
189,597 Re: Forum
179,263 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.005s) Memory: 0.9844 MB (Peak: 1.1377 MB) Zlib enabled. Server Time: 2019-01-21 13:53:02 UTC