12/12/01 08:01 AM
12/12/01 08:01 AM
N
NBuc100101@peoplepc.com  Offline OP
Junior Member
Joined: Oct 2001
Posts: 2
West Seneca, NY
We have a main circuit breaker (480 Volt, 3 phase) in an electrical enclosure. On the line side of this breaker we tap off and run number 12 wire to a 30 amp breaker which is located in the same enclosure. The 30 amp breaker is within 10 feet of the main breaker. We then take #12 wires off of the load side of the 30 amp breaker to feed another panel.
>
> Do we have a violation?

2017 / 2014 NEC & Related Books and Study Guides
Re: tap conductors #79299
12/12/01 08:56 AM
12/12/01 08:56 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Yes, you have violation(s).

#12 wire may be protected by not more than 20A. For 30A you must use #10AWG minimum. These ratings have been in table 310-16 for many code cycles and supercede any ampere ratings listed in the temperature columns.

Remember the tap rule is the total length of the conductors not the physical seperation of the devices.

Also how did you make the tap? It is a violation to put multiple conductors into a single lug (unless the lug is listed for that combination).


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,414 Are you busy
188,637 Re: Forum
178,341 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.005s) Memory: 0.9426 MB (Peak: 1.0603 MB) Zlib enabled. Server Time: 2018-11-13 22:25:07 UTC