Don,
I'll try to answer your numerous questions, although I'm not holding out any hope at convincing you...
______________________________________
So you are telling us that you have developed an electronic device that has a 50 to 100 year operational life!! I don't believe that is even possible. What is the failure mode of an AFCI?
Don(resqcapt19)
________________________________________
I don't believe I ever claimed that we had developed an electronic device with a 100 year operational life. What I said was that homes do not stay new, and that the panels in them are there for longer than the wiring is safe. Of course all electronics in homes would last longer with proper surge protection as IEEE recommends. Until it becomes code however, I don't expect that the industry will embrace surge protection as it should.
When you ask about the failure mode, I assume that you are asking what happens if the electronics go bad from surges. If this happens, the breaker will not trip when the test button is pressed, and the instructions are to replace the unit. This is the same as GFI breakers and receptacles, and obviously the key is to educate consumers on proper electrical maintenance. We maintain furnaces, gutters, woodwork etc. It's not too much to expect homeowners to push the test button. All that needs to be done is to give them the instructions that come with the unit rather than throwing them away. If they don't maintain the product, at least you've done what you can to provide a safe electrical system.
There is a bit of contradiction in your asking for a self-testing device while asking for an inexpensive unit. The reality is that we know that we cannot make these too expensive, or they will not be used. A self-testing AFCI or GFCI may be down the road, but it is cost-prohibitive at this time. If contractors are unwilling to spend $30 for an AFCI, I can pretty much assure you that they won't spend $60.
__________________________________________
1) I'm not convinced that they will function to stop the fires that the manufacturers say they will. They say they only work effectively on parallel arc faults. I've always been taught that 90% of electrical failures are at connections. This would be a series fault, not a parallel fault.
___________________________________________
I'm not sure what we will have to do to convince you that these are viable devices that will stop fires. There are a great number of folks that have studied the technology and have determined that it will save lives. The code making panel consists of every facet of the industry, contractors, builders, academia, etc. There is only one member from NEMA (National Electrical Manufacturer's Association). The process is there to keep any one body from dictating what gets through to the code. It is an arduous process to say the least, and a very important one. Without an electrical code, there would be virtually no new safety products developed. Manufacturers would not spend the money to develop new products unless the benefits could be mandated in some form or fashion. UL has a standard, CPSC and others have come out in favor of the technology, obviously it has been proven to folks that have analyzed it, so at some point you'll need to have some trust in the experts in your industry that represent you. For more on arcing faults from UL, go to
http://www.ul.com/about/otm/otmv5n3/labdata.html. _________________________________________
2) The fire statistics used to get these items into the code are faulty.
_________________________________________
The statistics that were used were from CPSC, the insurance industry and fire authorities. I'm not sure where you believe that better statistics exist, but if you know of any, I'd be happy to take a look at them.
_________________________________________
3) If they aren't fail safe they shouldn't be permitted on the market.
__________________________________________
Then you would continue this argument by stating that we shouldn't have GFCI, smoke detectors or sprinkler systems? All are not fail-safe.
Another issue that I would like to address is the glowing contact issue, and your use of Fire-Fighter products as a reason to question AFCI technology. First, our AFCI breakers are not only UL1699, but they are also UL 1053 for equipment ground fault protection, and will prevent the glowing contact phenomena. I find it ironic that you support the position of an unknown company like Fire-Fighter, but will not support the position of the company that invented the circuit breaker, and has more Ph.D. electrical engineers designing true world-class products.
Someone mentioned doing it the European way. Europe does not have whole house AFCI, they have earth leakage. Actually, some of the IEC manufacturers are looking at AFCI technology because of the problem they have with burning appliances. Europe does not have appliances that are as fire-resistant as the U.S. due to the environmentalist influence keeping chemicals out of the designs. They have a real problem, and they may soon turn to our technology to solve it.
I will try to answer Al and Motor-T over the weekend or late next week. I have to go try to sell some Arc Fault Circuit Interrupters next week.