ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Motion detectors and dimmers
by gfretwell. 09/20/18 04:02 PM
Extension cords
by annemarie1. 09/20/18 08:54 AM
Inspection camera help
by Bill Addiss. 09/19/18 10:50 PM
220/230/240V 60Hz Systems
by gfretwell. 09/16/18 12:37 PM
Acronis Backup 2017
by gfretwell. 09/16/18 12:46 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 24 guests, and 25 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
load calc's #78980
11/15/01 06:42 PM
11/15/01 06:42 PM
K
ken m  Offline OP
Member
Joined: Aug 2001
Posts: 58
south carolina
i'm doing a bid on a custom home with a heated square foot of 3400. gas heat with electric cooking appliances. question is, there are a total of 67 can lights throughout the house, would this be considered extra load and how would it be calculated? thanks for any comments. ken m

2017 / 2014 NEC & Related Books and Study Guides
Re: load calc's #78981
11/15/01 07:14 PM
11/15/01 07:14 PM
W
wolfdog  Offline
Member
Joined: Oct 2001
Posts: 135
Dallas,TX
Your question is not very clear. Which load are you concerned about? Heat,cool, or electric?

Re: load calc's #78982
11/15/01 08:49 PM
11/15/01 08:49 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Ken,

These lights are part of the general lighting load.

However, I wired a custom home once & the owner told me that everything would be turned on all night for his house warming party. I made sure that there would be no breaker trips.

If you are not bidding against Joe Lowball, include some extra circuits and extra capacity on the service. If you are bidding against Lowball Electric, you'd best stick to a code minimum job if you want to get this work.

Not knowing all the particulars, looks like this house should fit on a 200 amp service.

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: load calc's #78983
11/16/01 07:33 AM
11/16/01 07:33 AM
K
ken m  Offline OP
Member
Joined: Aug 2001
Posts: 58
south carolina
thanks tom, i calculated two different ways. first the general lighting load and figured about 140 amps then calculated by adding the extra load of about 50 of the can lights and figured the load to be about 170 amps. i will have plenty of room in a 40 circuit panel for some extra bkrs. thx again. ken m


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,359 Are you busy
187,292 Re: Forum
176,641 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9589 MB (Peak: 1.0897 MB) Zlib enabled. Server Time: 2018-09-22 03:20:35 UTC