Often times my project manager will insist that I use a gutter in lieu of a LB, to save money of course.
My question is how to interpret table(s)
373-6(a) and 373-6(b).If for example I were to enter the end plate of a gutter with 4 250mcm cables and exit through the back wall,I beleive I would use table (a). Would I go to the 4 wires per terminal column and use a 10x10 gutter with a lenght of 6x the conduit size?
Also If I bring my feeders into the top of a panel with lugs on the bottom do I need to use this table to determine if I have enough space to bring my cables down along the side and then bend 180 degrees up to the lugs?
thanks in advance, Barry

Horizontal Ad
#77896 07/20/01 07:13 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Barry,
Look at the exception to 373-28(a)(2). It tells you to use the "one wire per terminal" size from Table 373-6(a).
Don(resqcapt19)


Don(resqcapt19)

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
337,502 Are you busy
262,890 Re: Forum
243,177 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5