Why is it OK to have liquidtight flex and nonmetallic conduit (both having a PVC jacket ) under the raised floor, but not PVC with a ground conductor in it?
Joe Lusso, Electrical Plant Engineer Facilities Project Management 303.673.5248 phone 303.673.4551 fax email: LussoJA@louisville.stortek.com
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Doesn't 645-5 (d) (2) permit rigid non-metallic (PVC) conduit?
|
|
|
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
Redsy:
Yes, and the question is really not very clear. I have invited the person who asked this question to come aboard here on theis BB and look for the help he needs. I always bring these types of question here so we can all put our thoughts into the discussion.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
Originally posted by Joe Tedesco: Why is it OK to have liquidtight flex and nonmetallic conduit (both having a PVC jacket ) under the raised floor, but not PVC with a ground conductor in it? Most of the limitations on the use of PVC conduit inside buildings are the result of concerns about the fuel and smoke contributed under fire conditions rather than its performance as a raceway. -- Tom