Code Question #77550 06/21/01 08:14 PM
Joined: Jun 2001
Posts: 9
A
ampznvoltz Offline OP
Member
I'm adding a circuit in a metal building. The wall that I am working on is solid block(impossible to fish down the inside of it). I'm going to surface mount box and EMT pipe. ????Can I run MC cable to the pipe and skin it long enuf to get to recept box and run it down pipe. Of course I will use a MC connector with a rigid sleeve and then to EMT connector. THE REASON I WANT TO DO IT THAT WAY IS BECAUSE I CANT PUT A BOX IN THE CEILING BECAUSE THERE IS NO ACCESS-----I'M ONLY LUCKY ENUF TO FISH A WIRE THERE.When I get the wire thru the ceiling I will put it all together and then shove the sleeve and connectors in the ceiling so they cant be seen.Owner wants to see nothing but pipe.

2017 / 2014 NEC & Related Books and Study Guides
Re: Code Question #77551 06/21/01 09:43 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
ampsnvolts;
Welcome!
done it that way myself,just use the proper connectors, that' all. They even make MC or RX connectors to pipe , wiremould..

[Linked Image]

Re: Code Question #77552 06/22/01 09:31 PM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Ampz,

Not sure of this, but I may have heard that havintg this fitting in the ceiling (inaccessible) might technically be a violation.

How about just going through the conduit (no stripping) and go into a connector at the box. (pipe is loose and will slide up and down - just strap it to wall or use Mae Wests)

Bill


Bill
Re: Code Question #77553 06/22/01 09:43 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
mae wests?

Re: Code Question #77554 06/22/01 09:46 PM
Joined: Nov 2000
Posts: 2,236
sparky66wv Offline
Member
Would the screws of a BX connector (or NM for that matter) on a 4x4 box with a mud ring behind plaster also be a violation under this same argument?

Can a condulet with no splices be buried in the wall or ceiling under the same argument?

Just wondering (really wondering!)

-Virgil


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Code Question #77555 06/22/01 10:23 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline
Member
Biil: See Section 300-15(f) Fitting. A fitting identified for the use shall be permitted in lieu of a box or conduit body where accessible after installation and not containing spliced or terminated conductors.


and the NECH Commentary:

300-15(f)
Where a cable system makes a transition to a raceway to provide mechanical protection against damage. Section 300-15(f) permits the use of a fitting instead of a box. For example, where nonmetallic-sheathed cable that is run overhead on floor joists and drops down on a concrete wall to supply a receptacle needs to be protected from physical damage, a short length of raceway is installed to the outlet device box. The cable sheath is removed for the length of the raceway. The cable is then inserted in the raceway and secured by a combination fitting that is fastened to the raceway.

PS: Use of the correct fitting will allow visual inspection of the "redhead"


Joe Tedesco, NEC Consultant
Re: Code Question #77556 06/23/01 12:25 AM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Joe,

Thanks for the reference. I assume there would be no objections to the method I described? That would basically mean that the MC would be connected directly to the box via proper connector and EMT is just used as a sleeve and strapped to the wall?

Sparky,

Mae West: hmmm ... conduit supports? I don't know what to call them or why they're known as "Mae Wests" (except maybe the profile?) [Linked Image]

Joe? .. Anybody else know?

Bill


Bill
Re: Code Question #77557 06/23/01 07:41 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline
Member
Bill:

I always refer to them as "sleeves"


Joe Tedesco, NEC Consultant
Re: Code Question #77558 06/23/01 03:26 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
hmmm,
what would this 300-15(f) , as well as the definition of 'fitting' pertain to here? I could easily read many parts into this...
[Linked Image]

Re: Code Question #77559 06/23/01 05:25 PM
Joined: Jun 2001
Posts: 9
A
ampznvoltz Offline OP
Member
good idea Bill.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,432
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,017 Are you busy
205,012 Re: Forum
193,127 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3