#77546 06/20/01 09:19 PM
Joined: Dec 2000
Posts: 4,291
Member
In 2 cities right next to each other, Ufers are required to be installed in 2 different ways. One inspector wants the Cu tie wired right to the rebar. The other wants the Cu totally away from the rebar in the footing, but bonded together above the slab. Up until now I just have tried to remember which guy's city I'm working in.
Who's right???

[This message has been edited by electure (edited 06-20-2001).]

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#77547 06/20/01 09:53 PM
A
Anonymous
Unregistered
I think Ufer himself allowed the copper to be under the concrete. But in a wet area, the copper could possibly corrode away.

The place that is right is the one that requires a stainless steel rod to be welded to the rebar and left sticking out for the purpose of attaching the copper GEC.

#77548 06/21/01 05:31 AM
Joined: Oct 2000
Posts: 5,392
S
Member
what is the rationale? is the voltage gradient affected either way?

#77549 06/21/01 12:25 PM
Joined: May 2001
Posts: 176
W
Member
Searched "Ufer" and got an article published by Chris Scott in December of 1989 in Radio World magazine. According to the article, Mr. Ufer's findings were published in IEEE Transaction paper #63-1505.
"After much research and testing Mr. Ufer advised the Army to make connection to the steel bar that would internally reinforce the concrete foundation. He had determined that concrete was more conductive than all but the best soil, and that this improved semiconducting characteristic would enhance surface area contact with the surrounding soil. The wire ties normally used would be extra secure, and attention would be given to bonding or welding the lattice- type network together." We use this type system often doing design. The cage is wired together and a piece of CU is brought out to the steel column. This is all tied to the building ground loop, etc, to have a better than adequate grounding system.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Top Posters(30 Days)
BigB 4
triple 3
Popular Topics(Views)
302,813 Are you busy
232,001 Re: Forum
216,731 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5