430-33 #77326
05/20/01 08:50 PM
05/20/01 08:50 PM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,372
I am seeing many intermittent motors of various size over 1 hp without overload protection. I also see many 220V 1ph intermittent that disconnect only one hot leg.
Many of these have the maker's instructions pointing out 430-33.
My gut says something is fishy.

any input appreciated... [Linked Image]

2017 / 2014 NEC & Related Books and Study Guides
Re: 430-33 #77327
05/21/01 04:18 AM
05/21/01 04:18 AM
T
therain4  Offline
Member
Joined: Dec 2000
Posts: 38
Dunmore,Pa. U>S.A.
Sparky what application do you see motors controlled by only opening one grounded conductor? That sounds a little frightening . Who services these motors?art 430-103 says open all ungrounded supply conductors.

Re: 430-33 #77328
05/21/01 05:31 AM
05/21/01 05:31 AM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,372
i recently 'got into it' with tec support on a motor that serves a car lift.
there was only a momentary contact switch to serve one leg of a 220v 1 ph motor.

as 430-33 allows them to basically get away without overload protection , thus starter, there is no disco for the motor, except the breaker.

to me, this is an example of manufacturer's using the NEC to weasle around the expense of doing things right.

[Linked Image]

Re: 430-33 #77329
05/21/01 07:44 AM
05/21/01 07:44 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The motor controller is only required to open enough conducotrs to stop the current flow. On a single phase motor this would be 1 conductor, and on a 3 phase it would be 2 conductors. See 430-84.
430-103 applies to the motor disconnect, NOT the condroller, and is required to open all of the ungrounded supply conductors.

Sparky,
Your car lift installation requires a disconenct loacted in sight from the controller (430-102). If the momentary switch directly operates the motor, it is the controller. If the momentary switch operates a contactor, the contactor is the controller.

Don(resqcapt19)


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
BigB 3
Popular Topics(Views)
252,710 Are you busy
189,550 Re: Forum
179,224 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9593 MB (Peak: 1.0924 MB) Zlib enabled. Server Time: 2019-01-17 08:57:45 UTC