is it legal to run liquidtight flexible metal conduit as the raceway to feed a motor that sits directly next to a propane tank?
#76987 04/10/01 05:56 AM
what kind of motor ???
#76988 04/10/01 06:58 AM
What is the area classification? If it is Class 1 Div 2 then sealtight is ok. If it is Class 1 Div 1 then explosion proof flex is required at about $100.00 per for 1/2".
Don(resqcapt19)
Don(resqcapt19)
#76989 04/10/01 10:27 PM
Only if the area is classified as Class I, Div. II