URD Cable #76793
03/21/01 08:29 PM
03/21/01 08:29 PM
T
Tim M  Offline OP
Junior Member
Joined: Mar 2001
Posts: 4
I have spoke to supply houses who use the term URD for a direct burial type of cable similar to triplex. What is this found under in the NEC and UL Whitebook? Is it USE?

2017 / 2014 NEC & Related Books and Study Guides
Re: URD Cable #76794
03/22/01 06:16 AM
03/22/01 06:16 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,372
it comes marked USE/URD

[Linked Image]

Re: URD Cable #76795
03/22/01 03:41 PM
03/22/01 03:41 PM
B
Bennie R. Palmer  Offline
Member
Joined: Nov 2000
Posts: 72
Milwaukie, OR 97267 USA
Sparky must be in a hurry [Linked Image] This question appears often, and is asked quite frequently in the field. I have heard of inspectors not allowing cable assemblies identified as URD, for the reasons you state. The inability to locate any approval in publications, is the general reason.
URD, or underground residential distribution cable, can be USE, underground service entrance cable. When it is service entrance cable it is commonly, 3 conductors of Aluminum XHHW, with one conductor identified.
URD identified distribution cable can be medium voltage cable, in the range of 4.16 KV, to 34.5 KV. Of course this will not be marked as USE.

Re: URD Cable #76796
03/22/01 07:27 PM
03/22/01 07:27 PM
T
Tim M  Offline OP
Junior Member
Joined: Mar 2001
Posts: 4
Thanks. It helps to know what the abbreviations are. I then conclude URD/USE is used for primary and secondary for residential underground, and USE is secondary?

Re: URD Cable #76797
03/22/01 09:30 PM
03/22/01 09:30 PM
B
Bennie R. Palmer  Offline
Member
Joined: Nov 2000
Posts: 72
Milwaukie, OR 97267 USA
Tim: Only URD for 600 volts or less will be identified as USE.
URD for primary medium voltage will be PE, XLP, EPR, PVC, or CSP.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,279
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
253,284 Are you busy
189,904 Re: Forum
179,622 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.9666 MB (Peak: 1.1060 MB) Zlib enabled. Server Time: 2019-02-21 18:07:32 UTC