ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
220/230/240V 60Hz Systems
by djk. 11/21/18 09:04 PM
Single phase and what you call it.
by Scott35. 11/21/18 02:50 PM
sec cable code conflict
by HotLine1. 11/20/18 03:08 PM
This anti-theist is priceless!!!
by Texas_Ranger. 11/17/18 02:15 PM
High current GFI vs regular GFCI
by Texas_Ranger. 11/17/18 02:07 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 40 guests, and 24 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
bonding #76620
03/01/01 08:36 AM
03/01/01 08:36 AM
C
chuck  Offline OP
Member
Joined: Mar 2001
Posts: 10
decatur,il/usa
Where the code allows for installing a bonding conductor in mettalic conduit it states that the conduit must be bonded on both ends, question is if this is installed in mettalic conduit , attached to a metal building , does this reduce the requirement for bonding of the conduit?

2017 / 2014 NEC & Related Books and Study Guides
Re: bonding #76621
03/01/01 09:22 AM
03/01/01 09:22 AM
G
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
The bonding of the Grounding Electrode Conductor ( GEC) to each end of a metal raceway is required in 250 Part C, 250-64.

It appears the question has the GEC and the Equipment Grounding Conductor (EGC) inter-mixed.

Where a metal raceway encloses an EGC, I do not know where the NEC requires bonding each end of a metal raceway to the EGC. I also do not know where the NEC prohibits that practice.

250 Parts D, E, F, G, in general covers the equipment grounding required for systems less than 1000 volts.

Glenn

Re: bonding #76622
03/01/01 09:28 AM
03/01/01 09:28 AM
G
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
After re-read your question;

Each and every metal raceway enclosing the GEC must be bonded to the GEC at each end.

That would be Troughs, Conduits, Nipples, Junction Boxes, Switch and Meter enclosures etc.

Just by having the GEC metal raceway secured to a metal building structure would not accomplish this.

Glenn
Glenn

Re: bonding #76623
03/01/01 11:46 AM
03/01/01 11:46 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Chuck,

Welcome to our Forum.
Others here can give you a more detailed answer I'm sure, but I'll give it a try. If you're talking about the Grounding Electrode Conductor (GEC) it must be bonded to the conduit so that it can work properly in the event of a Fault. If it is not bonded and there is a sudden rise in current flow on the conductor fields may be set up that will oppose the current flow and effectively "choke" it.

Anyone feel free to correct me or add to this.

Bill

Re: bonding #76624
03/01/01 12:45 PM
03/01/01 12:45 PM
C
chuck  Offline OP
Member
Joined: Mar 2001
Posts: 10
decatur,il/usa
Gentlemen, I am talking about a water pipe bond from the service eqipment to the water service as we require locally.

Re: bonding #76625
03/01/01 01:59 PM
03/01/01 01:59 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Chuck,

Yes, that is what we are talking about if I understand it correctly. The conductor from the service that is connected to the water pipe runs through a metal conduit. this must be bonded at both ends as described in the code section mentioned. Over at the IAEI forum there was a recent thread with questions regarding types of clamps used and there are some pictures there too. take a look.
http://www.iaei.com/ubb/Forum1/HTML/000019.html

I hope this helps,

Bill


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Top Posters(30 Days)
djk 3
Popular Topics(Views)
251,688 Are you busy
188,815 Re: Forum
178,533 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.006s) Memory: 0.9767 MB (Peak: 1.1222 MB) Zlib enabled. Server Time: 2018-11-22 10:48:30 UTC