bonding #76620 03/01/01 09:36 AM
Joined: Mar 2001
Posts: 10
C
chuck Offline OP
Member
Where the code allows for installing a bonding conductor in mettalic conduit it states that the conduit must be bonded on both ends, question is if this is installed in mettalic conduit , attached to a metal building , does this reduce the requirement for bonding of the conduit?

2017 / 2014 NEC & Related Books and Study Guides
Re: bonding #76621 03/01/01 10:22 AM
Joined: Jan 2001
Posts: 75
G
Glenn Offline
Member
The bonding of the Grounding Electrode Conductor ( GEC) to each end of a metal raceway is required in 250 Part C, 250-64.

It appears the question has the GEC and the Equipment Grounding Conductor (EGC) inter-mixed.

Where a metal raceway encloses an EGC, I do not know where the NEC requires bonding each end of a metal raceway to the EGC. I also do not know where the NEC prohibits that practice.

250 Parts D, E, F, G, in general covers the equipment grounding required for systems less than 1000 volts.

Glenn

Re: bonding #76622 03/01/01 10:28 AM
Joined: Jan 2001
Posts: 75
G
Glenn Offline
Member
After re-read your question;

Each and every metal raceway enclosing the GEC must be bonded to the GEC at each end.

That would be Troughs, Conduits, Nipples, Junction Boxes, Switch and Meter enclosures etc.

Just by having the GEC metal raceway secured to a metal building structure would not accomplish this.

Glenn
Glenn

Re: bonding #76623 03/01/01 12:46 PM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Chuck,

Welcome to our Forum.
Others here can give you a more detailed answer I'm sure, but I'll give it a try. If you're talking about the Grounding Electrode Conductor (GEC) it must be bonded to the conduit so that it can work properly in the event of a Fault. If it is not bonded and there is a sudden rise in current flow on the conductor fields may be set up that will oppose the current flow and effectively "choke" it.

Anyone feel free to correct me or add to this.

Bill


Bill
Re: bonding #76624 03/01/01 01:45 PM
Joined: Mar 2001
Posts: 10
C
chuck Offline OP
Member
Gentlemen, I am talking about a water pipe bond from the service eqipment to the water service as we require locally.

Re: bonding #76625 03/01/01 02:59 PM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Chuck,

Yes, that is what we are talking about if I understand it correctly. The conductor from the service that is connected to the water pipe runs through a metal conduit. this must be bonded at both ends as described in the code section mentioned. Over at the IAEI forum there was a recent thread with questions regarding types of clamps used and there are some pictures there too. take a look.
http://www.iaei.com/ubb/Forum1/HTML/000019.html

I hope this helps,

Bill


Bill

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 74
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,713 Are you busy
204,953 Re: Forum
193,058 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3