Grounding Conductor #76618 02/28/01 05:59 PM
Joined: Feb 2001
Posts: 1
J
jsb55 Offline OP
Junior Member
Section 250-91(b) (1996 NEC) allows the use of emt as the grounding conductor of a circuit. My question concerns whether the common type emt fittings will provide continuity or if some type of bonding connector should be used? What is normal in the industry?

thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding Conductor #76619 02/28/01 06:40 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
EMT fittings will safely carry ground fault currents At least the steel ones will, some of the zinc die cast don't perform as well, mainly because the locknuts sometimes won't penetrate the paint on some boxes or fixtures.

Many electricians around here also install an equipment grounding conductor inside the conduit. We've all seen fittings that have loosened or have had the conduit pulled out & when that happens, there is no ground downstream from the break.

I personally pull in a seperate equipment ground in any conduit likely to get abused. I don't bother to do this with conduits that are 20 feet in the air, but once you drop down to 10 feet or so they can be easily damaged.


Few things are harder to put up with than the annoyance of a good example.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,700 Are you busy
204,940 Re: Forum
193,051 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3